Neff microwave oven
DP
10 Dec 2003
Glasgow
I have this integrated microwave oven.
Couple of days ago I pulled the Beko condensing tumble dryer out to clean behind it.
The microwave is fitted above the twin oven against the opposite wall
While the dryer was out of its slot under the worktop, there was a bang and the power tripped.
Restored the power and commenced to set the microwave clock to correct time- breaker tripped again.
I looked at the mains filter inside the oven. No damaged parts. Caps measured the stamped value. Resistance across the L and N is 77k ohms. Disconnected the lead going to power supply and plugged in the microwave that only had the filter connected- nothing beyond. No ibreaker tripped again
Fuse on the filter board is intact.
Is it realistic to repair the oven by self or by Neff. Breaker tripping seems to suggest leakage to earth issue or am I talking rubbish
Breakers are MBCOs
Thanks for looking at the post
So the dryer is a red herring and nothing to do with the fault ?
Did you try the microwave with the dryer disconnected and vice versa. It is unclear, as Wayners suggests ,which, if either, is the problem from your discription.
You need to test the resistance between live/neutral and earth as well as live and neutral
If it is the microwave then it is unlikely to be a diy repair but it's worth asking Neff if they do a fixed price repair before you decide to replace it
  • Thanks
Reactions: DP
What caused the trip?
Trip caused by microwave.
Yes dryer had zilch to do with the tripping
Did check the resistance. Is as indicated in the post between L&N
No Reading when L or N measured to E
Meter used is Fluke 289
Will give Neff a call and ask for FPR. Thanks for that pointer
Thought as much re DIY repair. Took the cover off to see if peripheral component like the suppressor was the issue. It is not a short circuit else the fuse would have blown, but was quite a thump when the power was interrupted ( twice)