But reg 411.4.9 calls for fault current to be dealt with by the overcurrent protective device, a fault causting fault current to flow can be phase to earth.Spark123 said:So the fault can be phase to earth and still needs to be dealt with by the fuse/MCB? If this is the case then the max efli will still be governed by the fuse/mcb surely?
No, the phase to earth fault is dealt with by the RCD. This will disconnect less than 0.4 seconds, even at 5xIn. Thats why EFLI is raised to 1667, as per table 41.5, and 411.5.3 (i) and (ii) being met.
An RCD is not an overcurrent protective device.
I know that an RCD is not an OPD.
Spark123, yes, a fault causing fault current can be phase to earth. I accept that. I thought it pretty clear that the RCD is providing protection against a phase to earth fault.
Please bear with me and read 411.4.9, then chapter 43 (for the requirements of the OPD) to which it refers, and then the definitions again, study table 41.5 and its associated notes, and then maybe you will
agree with me. good fun this eh ?