Earth Block Question
Sorry, just to clarify we moved into after it had had the extensions and questionable Electric work.... ;-)
Did the guy you dealt with do a Ze?
Zs readings are all very well, but that will not necessarily show up an earthing problem if you have a good earth path provided by something else.
I see 100's of subterranean TT supplies where folk have tried to get an earth connection off the sheath just like your arrangement, but because the sheath is not connected to earth, the reading is non-existent.
Definately get the DNO to fit a proper earth connection to that cable. It will be sweated on, or now they sometimes use a spring arrangement that wraps round the sheath.
Thanks Securespark, On the test sheet there is a measurement under the heading:
External Loop impedance, Ze 0.31 ohms.
I will get the Suppliers out to put the connection on properly, I am now quite concerned about it.
So if the DNO would also connect to the sheath (but with a correct connection). I assume then that it is ok to take an earth from the sheath, just not ok to use that type of connector?
