1.5mm2 cable for single socket?

Ahh ok a fused device which will limit the load to a maximum of 13A regardless of how many heaters you decide to plug in to it then.

or a 4 way splitter with 3 heaters in addition to the automation.

What exactly was the point you were failing to make?
 
Ahh ok a fused device which will limit the load to a maximum of 13A regardless of how many heaters you decide to plug in
Not all 4 way splitters are fused, though their plug will have a 13 amp fuse. 13 amp fuses don’t limit the current to 13 amps. They will take considerably more before failing.
 
Not all 4 way splitters are fused, though their plug will have a 13 amp fuse. 13 amp fuses don’t limit the current to 13 amps. They will take considerably more before failing.

Will a 13A fuse fail before a 1.5mm² cable?
 
If you don't feel able to answer that question without risking lying, one has to wonder what questions relating to anything electrical you know enough about to be able to answer.
All the ones I do answer.
 