It is permitted that 1.5sq.mm cable can be used to spur off a ringmain.
You cannot spur off a spur unless the original spur is from the load side of a 13a FCU.
This 1.5sq.mm is protected by the ringmain fuse of 32amps yet the ccc of the cable is approx. 17-20amps.
This spur feeds a twin socket capable of pulling two loads of 13amps therefore 26amps.
What happens if this occurs?