2.5mm cable into 1.5mm ?!

Interesting insight, thank you.

In my head, I can see myself telling me "the smaller cable it is, the less power you're allowed to use" :LOL:
 
The limiting factor in this case is most likely the B6 MCB in the consumer unit rather than the cable.

You don’t want to plug a hoover or circular saw into that socket but all the gear you mentioned is perfectly fine.
 
The limiting factor in this case is most likely the B6 MCB in the consumer unit rather than the cable. You don’t want to plug a hoover or circular saw into that socket but all the gear you mentioned is perfectly fine.
Indeed. 1.5mm² cable would happily carry the current of two or three "hoovers" or circular saws, but a 6A MCB would not be at all happy about that :-)
 