One is for a whirlpool bath and other for the controls in a power shower run of a combi. Both say in the instructions to run them of a 13amp fuse spur.
I moved bathroom into one of the bedroom. The 2.5 mm socket ring cable is under the floor I was thinking of braking into this with a JB then adding to cables running to fuse spurs of this.
You would have to use a maintenance free juntion box as it will be inaccessible. And you would need to take 2 separate spurs from the ring, as each of the 2 could use a total of 26amps, which is too much for a 2.5mm T&E.....
You would have to use a maintenance free juntion box as it will be inaccessible. And you would need to take 2 separate spurs from the ring, as each of the 2 could use a total of 26amps, which is too much for a 2.5mm T&E.....