if you put a fused spur on the ring then you can run multiple spurs off it.
Can you run multiple spurs off a ring without a FCU if you do it in say 4mm t&e?

in other words can you have a circuit which is part ring part radial?

also is it allowed to have 2 ring mains in 1 mcb?
 
Sponsored Links
if you put a fused spur on the ring then you can run multiple spurs off it.

Correct.

Can you run multiple spurs off a ring without a FCU if you do it in say 4mm t&e?

No.

in other words can you have a circuit which is part ring part radial?

In other words no.

also is it allowed to have 2 ring mains in 1 mcb?

No.

Are you really sure you are competant to be carrying out electrical installation work for profit?
 
the CU already has 2 rings in the mcb.
obviously a lot of cowboys out there who do dodgy work.
at least i get the advice first!!
 
Can you run multiple spurs off a ring without a FCU if you do it in say 4mm t&e?

No. But strangely enough, you can do it the other way around.

You can connect 2.5 to a 32A 4mm² radial providing it only feeds one outlet.
 
Sponsored Links
now i may be wrong

Yes you are.


IMGP2837.jpg
 
yes i just went and checked. :LOL: its good to see tho i can take a 2.5 spur off the ring direct from the board.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top