2 way switch, 2 circuits, arced neutral

Discussion in 'Electrics UK' started by Beneop, 15 Jun 2020.

  1. Beneop

    Beneop

    Joined:
    15 Jun 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi all,
    I have just moved into a house and went to use the light switch last night, it buzzed then shorted. Took the switch off this morning and there looks to have been an arc across to neutral(?)

    This switch has 2 feeds, looking at it the right switch controls the downstairs hall, the left switch is a 2 way to control the landing.
    There are a few cables, it was a blue with red band that seems to have arced, this was connected to the top L3 point, my question is, is the wiring ok? I mean the hallway switch worked fine as I've used that before now, secondly, where is the blue wire meant to go so the 2 way works properly.

    Hopefully the photos will help.
    Thanks

    20200615_103012~2.jpg 20200615_103416.jpg 20200615_103050.jpg 20200615_104225.jpg
     
    Last edited: 15 Jun 2020
  2. Sponsored Links
  3. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    6,494
    Thanks Received:
    496
    Location:
    London
    Country:
    United Kingdom
    It goes in one of the L3s. But as we don’t know which terminals belong to which switch from your diagram I can’t say which L3.
     
  4. Beneop

    Beneop

    Joined:
    15 Jun 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    15922173046568197949064943968162.jpg 15922173046568197949064943968162.jpg 15922171696169199937942111464718.jpg Thanks for the reply.
    New photo attached.

    This is an old switch, l1,l2,l3, no com. Should the yellow not be in l1?
     
  5. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    6,494
    Thanks Received:
    496
    Location:
    London
    Country:
    United Kingdom
    It goes in the L3 which is burnt. But you may need a new switch. There is no reason for the yellow wire to be wrong if you have not touched it.
     
    • Like Like x 2
    • Thanks Thanks x 1
  6. Beneop

    Beneop

    Joined:
    15 Jun 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank, just put the blue into L3 on that section. Works fine.
    Seems to have arced as the exposed wire was too long/not fully in as opposed to my thinking it was connected incorrectly.

    Appreciate the help
     
  7. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,105
    Thanks Received:
    2,066
    Location:
    Oxfordshire
    Country:
    United Kingdom
    You still should replace the switch.
    Oh and before anybody else mentions it
    There are no neutrals in that switch. just because a wire is blue doesn’t make it a neutral. See that red sleeve on the wire? That tells you that the wire can be live.
     
    • Thanks Thanks x 1
    • Like Like x 1
  8. Sponsored Links
  9. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    2,224
    Thanks Received:
    292
    Country:
    United Kingdom
    But don't you admire Winston for not pointing that out?
     
    • Like Like x 2
  10. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,105
    Thanks Received:
    2,066
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Sorry, my admire facility is broken. Can’t get a new one cos the shop’s closed:sneaky:
     
    • Like Like x 1
  11. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    2,224
    Thanks Received:
    292
    Country:
    United Kingdom
  12. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    46,751
    Thanks Received:
    3,029
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    It might now be open again, as of today :)

    Kind Regards, John
     
  13. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    4,552
    Thanks Received:
    333
    Location:
    Kent
    Country:
    United Kingdom
    Indeed... But in the circumstances, which is offering appropriate and good advice, it would have been a fair comment to mention it's not a neutral.

    AND a thankyou to Beneop for the pictures, making drawings and the feedback.

    Yes it really is a good idea to replace the switch having had such an incident.
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page