Thanks for the link. I had been looking at the Viessman 100 model.
You are quire correct, the 200 model uses proprietary controls, so you are tied into them if you want weather compensation.
EDIT: Would I be right in thinking that the weather compensation controllers function by actually analysing the temperatures in the house and outside, and adjusting boiler flow temps accordingly to achieve condensing mode most often and reduce cycling?
"Pure" weather compensation just looks at the outside temperature. It works on the basis that heat loss is more or less proportional to difference between outside and inside temperature, and radiator output is approximately proportional to the mean water temperature. So you need a high flow temperature for low outside temperatures, and low flow temp for high outside temps and an inverse linear relationship between the two. More sophisticated systems have a curve relationship, rather than linear.
The other thing that has to be considered is changes in the required internal temperature. If the system has been set up by the installer for a 20C internal temperature and the home owner decides to change it to 22C. The "curve" will have to be changed. On simple systems this would mean an installer visit, but on more sophisticated ones the owner will just have to dial in the new indoor temperature and the curve will be automatically recalculated.
Have you read the
Viessman Guide to Weather Compensation
As for achieving condensing mode more often, this will be true when the weather is warmer. But if you want to maximize the time when the boiler is condensing, the system has to be designed from scratch to work with lower temperatures as condensing does not occur until the return temperature is below about 55C. This means that radiator outputs will be lower than given in manufacturers' literature, so larger rads will be required.
If you are seriously considering weather compensation, take a look at the Remeha Avanta boilers. They all have WC facilities but you are not limited to Remeha controls as they adhere to the Opentherm standard, which means that any Opentherm control can be used.
As for zoning I doubt if you will see any benefit - unless you have a very large house; thermostatic valves will probably be all that is required.