    On the 3 phase board will there be 3 Ze's? bit confused as on schedule of test results it looks like only one Ze is asked for
     
  2. Sponsored Links
  3. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,684
    Thanks Received:
    278
    Country:
    United Kingdom
    No, the Ze is the worst case reading (highest impedance) you get after you have tested the fault loop between the means of earthing and each of the three phases in turn

    Same kinda thing with the PFC, just the one number to write down, its the worst case (highest ka) out of the three P->N PSSCs and three P->E PEFCs, *doubled* (this is to take account of faults involving more than one phase)

    Don't try and measure PFC phase to phase unless you are sure that the instrument is designed to measure phase->phase!... best stick with the single phase measurement and doubling just incase
     
  4. FingRinal

    FingRinal

    Joined:
    22 Feb 2008
    Messages:
    658
    Thanks Received:
    0
    Country:
    United Kingdom
    2391 Practical is a bit like a driving test. The examiner is hoping for a easy time with a group of 'safe' and competent electricians. Start flapping about and looking nervous and you'll attract more attention. Start off in the right manner, let him see your safe isolation procedures and confidence with your test kit and you'll be off on the right foot. The examiner will start to focus elsewhere as basically he is the safety man. You might make the odd minor mistake which might 'prompt' a question from the examiner. If you are in control and recover with confidence they will be over looked.

    If you look like you are out of your depth, start flapping or are too tense you might fail purely on the basis of safety. The examiner won't want to take any chances with a live board.

    So, keep calm, keep logical and keep to the basics. There isn't a lot of slack time so don't hang around.

    Also, don't assume that the test rigs are fault free. Some take a right hammering or the previous bloke might have left a few faults on. So, if you get a few funny readings don't assume that you are wrong as it could be the rig.
     
  5. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,684
    Thanks Received:
    278
    Country:
    United Kingdom
    Or an over zealous technician with too many wirewound resisters to make the readings resemble a real installation, Zs for the ring final ended up at about 2 ohms!
     
  6. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    thanks for the reply-so its the highest Ze out of the 3 phase-earth loop tests I write down-cheers
     
  7. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,684
    Thanks Received:
    278
    Country:
    United Kingdom
    Aye,

    Main switch off, earthing conductor disconnected from met, tester earth lead clipped onto earthing conductor, probe the line side of tester onto L1 on incomming side (probe neutral onto neutral as well if you tester needs one), take reading, move the line side onto L2, take reading, then L3, take reading

    Then take the highest worst case one, so if I got 0.31, 0.35 anf 0.33, then I'd write down 0.35 as thats worst case (highest impedance)

    Reconnect means of earthing before re-closing main switch!

    Do you have a copy of GN3?
     
  8. Sponsored Links
  9. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    Yeah got GN3 but didn't explain the three phase situation all that clearly,so whatever reading I get for PEFC I just double the highest one and put that in the Ka box? cheers
     
  10. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,684
    Thanks Received:
    278
    Country:
    United Kingdom
    Not quite, take the highest of all the PSCC readings and the PEFC readings you get (although normally PSCC readings will be higher than PEFC ones), then double it for a fault involving mutiple phases this is what you write in the PFC box

    (some 3-wire testers let you take PSCC and PEFC by just toggling a button)

    PEFC - Prospective Earth Fault Current
    PSSC - Prospective Short Circuit Current

    PFC - Prospective fault current (for either type of fault)
     
  11. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    thanks for that, so double the highest PSSC will be the answer-remember lecturer saying u don't have to bother with PEFC as PSSC will be higher, cheers
     
  12. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,530
    Thanks Received:
    374
    Country:
    United Kingdom
    that is bad advice, PSSC will usually be higher but it is not something you can rely on.

    Also while the double it rule has a fairly substantial safety margin it is still IMO better to read the real phase-phase PFC value if your tester can do it (think of the case of a bad neutral for example).
     
  13. alex28

    alex28

    Joined:
    6 Aug 2007
    Messages:
    27
    Thanks Received:
    0
    Country:
    United Kingdom
    just failed practical on two out of four assessments-only spotted 11/12 faults on the board and left key in main switch padlock when doing motor starter circuit! gutted because was going ok, got Ze and PFC right for 3 phase system and passed the other two assessments (insulation resistance and working out Zs for the MCB's using rule of thumb & formula method)
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page