25mm 120 amp 3phase question

Sponsored Links
Yes, it is a re-arranged formulae of the one I posted above lol.
I'm not too sure on it taking 5s> to disconnect??
 
Sponsored Links
hehe i realised that after i posted


the formula says that 25mm can take 600 amps for 23 secs, and the fuse will blow in less than half that time , right >?
 
You're about there, my only query would be having an earth fault last longer than 5s.
 
oh yeah thats not really allowed is it ?



:oops: can i ask where the 600 amps came from in ricicle's post

415/0.8 = 518amps
 
I think he used 240/0.8 = 300A, then doubled it up, although for an earth fault would only be 240v hence I think you should use 300A??
 
Jim2287 said:
hehe i realised that after i posted


the formula says that 25mm can take 600 amps for 23 secs, and the fuse will blow in less than half that time , right >?

Yes, in the event of a 600A fault it would take a 25mm² 70°c pvc cable 23 secs (22.96) to reach its final limiting temp of 160°c, but this level of fault would clear a 125A BS88 in 10 secs so no thermal damage would occur to the cable
 
300 amp fault on 125amp BS88 take 300 seconds to blow :eek: if i understand the graph right


then ...

IxI = 300amps x 300 = 90000
xt = 300secs = 27,000,000

divide by K of 47 for steel trunking = 574468

Square root = 757mm + cable :oops:



either ive done it completely wrong or you wouldnt install 125 amp fuse on a system with 0.8ohms Ze ?
 
Spark123 said:
I think he used 240/0.8 = 300A, then doubled it up, although for an earth fault would only be 240v hence I think you should use 300A??

t = K²S²/I² = 115²25²/300² = 8265625/90000 = 91.4 secs

125A BS88 will clear a fault of 300A in 300secs so in the case of a Ze of 0.8 and and an earth fault of negligible impedance the 25mm² would not comply as the conductor would have reached its limiting temp in 91.4 secs

Jim your Ze needs to be checked to see if it lower than 0.8!!
 
yep im sure it is less than 0.8 ohms, but im using that as the maximum for TN-S for my learning


you guys have been a great help, thanks
 
Jim2287 said:
300 amp fault on 125amp BS88 take 300 seconds to blow :eek: if i understand the graph right


then ...

IxI = 300amps x 300 = 90000
xt = 300secs = 27,000,000

divide by K of 47 for steel trunking = 574468

Square root = 757mm + cable :oops:
It is the square root of I²t then divide by K, the answer is about 110.
Edited as everyone it typing too fast :LOL:
 
Just re-checking, table 43A (K values) only applies for disconnection times up to 5 secs anyway:any longer and you need to consult cable maker.
I would say that 0.8 is a rather pessimistic value for TN-S anyway unless anyone would like to correct me so the fault currents and thus disconnection times would be quicker.

The values I normally work with are favourable as we have 6 1000Kva transformers of our own so Ze is always low ;)
 