possible to spur of this and im guessing u would have to spur off using 4mm cable, is there a limit on spurs? can u spur 2 sockets in series off a socket.
ty, sorry bad terminology on my part, spur of a spur i should have said
Many other makes you will find you can't get two 6mm cables to fit. Because most of the Ali-tube cable to BS 8436 is rated at 90 deg C not 70 deg C it does have a higher rating and I was surprised to see Table 4D5 does not have an equivalent for Ali-tube which since Ali-tube is made special for stud walls one would have expected it to have been included.Terminal capacity:
Live, neutral & earth
3 x 2.5mm2
3 x 4mm2
2 x 6mm2 (standard)
And it does not have a rating of (30 ÷ 0.725) for any installation method.I have questioned the use of 4mm cable on 32A radials many times as although clipped direct it has a ratting above 32A buried in a wall it does not.
I'm not surprised - 4D5 is for BS6004 flat cable.I was surprised to see Table 4D5 does not have an equivalent for Ali-tube which since Ali-tube is made special for stud walls one would have expected it to have been included.
See the warning note on any of the tables that have ratings for 90° cables - terminating them in accessories only rated for 70° is also another story.So 45 x 0.725 = 32.625 so no reason why Ali-tube 4mm cable clipped direct should not be used on a 32A fuse on a radial circuit. So nothing wrong with the BS 7671:2008, Corrigendum (July 2008) diagram although using 70 deg C twin and earth is another story.
There's no such thing as a spur from a radial circuit, so yes, as long as you stick with 4mmsq (or other appropriately sized conductors for volt drop etc) then it's no problem to come off the radial to as many sockets as you like.
It depends.I assume a 20A fuse would be fine for 4mm ?