315 VAC?

You can safely bet your burgeoning bikini waxing client database that I'll be examining the certificate with all the cynical finesse of Frank Abagnale Jr.
 
What's tp say that the neutral hasn't become detatched etc after the supply was installed / inspected tested?
 
I'm making no assumptions, but, even ignoring all the other little indicators, I doubt very much that the CU earth bar installed itself badly and that a screw from the SWA enclosure lid unwound itself.
 
try and get back to the point where that flats single phase supply branches off the three phase system and do voltage and do loop impednace measurements on all combinations (prefferablly including phase-phase measurements but check your tester is capable of taking theese before you try it).

a bad neutral in the three phase part of the system is my bet.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top