Hi, I know this is notifiable, but friend's brother is gonna do this [edit: in his house] anyway, so we might as well get it right.
Please don't advise on wiring from the CU to outlet - I know how to calculate and check all that, it's just the last bit that puzzles me.
Beko recommends the cooker be wired to the cooker connection plate in H05W-Fg 5 x 1.5mm2 cable or 3 x 4mm2 "or equivalent".
Sure, it's a 9.4kW total consumption, so we could use diversity to get 20.3A requirement [based on 230V which is how I assume I should do it?] (?).
Since the cooker has only 3 terminals (L+N+CPC), I can't see why you'd bother using 5-core. To double up the L+N perhaps? Still that only gives us 20A current capacity (not sure about that figure tbh).
Wouldn't it be better just wired in a bit of 6mm T+E, even though that's not ,technically, flexible?
Surely the reference to 5 core 1.5mm2 is a typo? Would anyone here consider using something that thin (especially given the probable warm environment), even though there would be two live and two neutral cores?
Please don't advise on wiring from the CU to outlet - I know how to calculate and check all that, it's just the last bit that puzzles me.
Beko recommends the cooker be wired to the cooker connection plate in H05W-Fg 5 x 1.5mm2 cable or 3 x 4mm2 "or equivalent".
Sure, it's a 9.4kW total consumption, so we could use diversity to get 20.3A requirement [based on 230V which is how I assume I should do it?] (?).
Since the cooker has only 3 terminals (L+N+CPC), I can't see why you'd bother using 5-core. To double up the L+N perhaps? Still that only gives us 20A current capacity (not sure about that figure tbh).
Wouldn't it be better just wired in a bit of 6mm T+E, even though that's not ,technically, flexible?
Surely the reference to 5 core 1.5mm2 is a typo? Would anyone here consider using something that thin (especially given the probable warm environment), even though there would be two live and two neutral cores?