Discussion in 'Plumbing and Central Heating' started by KevinPR, 16 Oct 2021.

  1. KevinPR

    KevinPR

    Joined:
    16 Oct 2021
    Messages:
    3
    Thanks Received:
    1
    Country:
    United Kingdom
    For last couple of weeks heating/radiators havent been turning off.

    Checked, and it seems one of the motorised valve actuators (Honeywell) is alway open. (No resistance on the little lever) The metal casing is very hot compared to the other 2 so an wondering if the motor is running constantly?

    The only time it closes is if I kill the power to it completely. When power is off the resistance returns to the little lever) As soon as it's powered on again it opens...

    Is this likely to be the actuator at fault (if so I'll just replace it) or is it likely that something else could be causing the motor to be constantly on?
     
  2. Sponsored Links
  3. jackthom

    jackthom

    Joined:
    14 Feb 2007
    Messages:
    1,365
    Thanks Received:
    242
    Location:
    Northumberland
    Country:
    United Kingdom
    No it is not stuck and is opening and closing when the system is powered on and off.
    It sounds like the acuator is opening because it's getting switched on by something else in the system, possibly a problem with the room thermostat not switching off.
     
    • Thanks Thanks x 1
  4. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    9,059
    Thanks Received:
    2,421
    Location:
    North
    Country:
    United Kingdom
    Deleted.
     
    Last edited: 16 Oct 2021
    • Thanks Thanks x 1
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,507
    Thanks Received:
    9,708
    Location:
    Lanarkshire
    Country:
    United Kingdom
    it is not the motor you are getting a supply to the motor from somewhere, post pics of your programmer, thermostats and boiler facia
     
    • Thanks Thanks x 2
  6. Sponsored Links
  7. KevinPR

    KevinPR

    Joined:
    16 Oct 2021
    Messages:
    3
    Thanks Received:
    1
    Country:
    United Kingdom
    It's the bottom valve. Only turns off when power is cut.
    Programmer has heating switched off.
     
    • Thanks Thanks x 1
  8. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,507
    Thanks Received:
    9,708
    Location:
    Lanarkshire
    Country:
    United Kingdom
    The boost LED is illuminated on your programmer, looks like that is the culprit, you could try re-setting the programmer if you cant get the Light to turn off, there is a small hole with RS you push a paper clip or similar in there to reset to factory settings
     
    • Thanks Thanks x 1
  9. KevinPR

    KevinPR

    Joined:
    16 Oct 2021
    Messages:
    3
    Thanks Received:
    1
    Country:
    United Kingdom
    I'm able to turn off the boost indicator (that was referring to water) it's not resolved it unfortunately
     
  10. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,507
    Thanks Received:
    9,708
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Then its multi meter time to find out where the voltage onto the brown wire on the problem valve is coming from
     
    • Thanks Thanks x 1