Another spur / additonal Socket question

Joined
28 Apr 2008
Messages
68
Reaction score
0
Location
Leeds
Country
United Kingdom
Hi All,

I have FCU running from a socket in a bedroom with the output cable going into the loft and powering three sockets.

Can I add a junction box before the cable goes into the sockets (but after the FCU?) - I want to add a single socket to power an LED Tv. I am guessing I can't run two output cables from one FCU? The problem is that the sockets in the loft are very far away from where I need the TV

Thanks
 
Can I add a junction box before the cable goes into the sockets (but after the FCU?)
As long as it's accessible for inspection, or is of a maintenance free type.


I am guessing I can't run two output cables from one FCU?
Depends on what the manufacturer says about the capacity of the terminals.
 
"Depends on what the manufacturer says about the capacity of the terminals."

Good Answer.

Mind you, what did they say about 2 x 4.0mm and 1 x 2.5mm or 3 x 4.0mm conductors for BS 1363 accessories before appendix 15B appeared in the "Bumper Book of Fun"?
 