Could somebody do the calculations?What happens when there's a fault ?
Could somebody do the calculations?What happens when there's a fault ?
Someone would need to make up a scenario - supply impedance, loop impedance of the circuit, type of fault, ... If you stick 230V across one end of a 2m bit of 0.5mm cable with a dead short at the other end then there's little doubt a 16A fuse or breaker will pop "quite quickly".Could somebody do the calculations?
Not if you actually include the cable in your calculations.Isn't that over-complicated?
I have. 2.875 is very high.Not if you actually include the cable in your calculations.Isn't that over-complicated?
That leaves 2.689Ω for the circuit.My out of date BRB gives the resistance of 0.5A flex as 93mR. So say a 2m flex, that's 0R186.
Using your figures (if I'm correct) another 7.1 metres.Now, how much 0.5mm cable does there need to be before the B16 doesn't trip "instantly" ?
No.Never seen a fault that wasn't a "hard short" ?
Far from it - all you've proved is that with a short cable it should be.Not sure where we are going.
Have we not proved small (0.5mm²) appliance leads would be satisfactory?
Well, exactly. I thought that's what we were discussing.Far from it - all you've proved is that with a short cable it should be.
Obviously - same with any cable.Add in some extra flex and the resistance of the circuit increases, reducing the fault current.. At some point the breaker no longer trips "instantly" but then needs the thermal element to trip. The energy dissipated in the flex during the trip time could be considerably more than your initial calculation.
Not wasting time. Elfen safe tea.However, if you are correct, then we've been wasting our time all these years using fuses in our plugs
Did I do the sums correctly?you even went as far as saying 0.5mm cable would be OK on a 32A MCB.
Strange how people often think threads pointless after contributing several posts.It is also a rather pointless thread of discussion since we have our BS1363 fittings on RFCs (or sometimes 4mm radials), and they have their different ones on radials. That isn't likely to change any time soon.
It is also a rather pointless thread of discussion