Hello

What size armoured cable will I need to run about 150m and what would the maximum load it could take be. I will be using an electrician but I am just looking at the options and pricing the work up.

Thanks

Barnman
 
Sponsored Links
You size the cable on the load you need to draw, not the other way around!

Edit: well too slow.
 
Sponsored Links
I understand - so lets assume 10KW. The cable will be buried in the ground.
 
OK - works out expensive which is why I wanted to check this. What about 5KW?
 
Half that - but that will mean 16mm² (no 12.5) - but then you can have 6.3kW, 27A.

Before anyone says this is way over the volt-drop limit for lighting, does it matter?
 
That would be nice but as it is a stable with a couple of storage rooms etc I will live with the limitations depending on the cost. It will need lighting, maybe a kettle, maybe a heater but I think 6.3KW will be more than enough. If I ran 10mm cable, this would save about £200 but what load would this take? Any lower I imagine I will be restricted to lights only.
 