Back Box Size (but now about cable size)
  • Thread starter Thread starter cb9002
  • Start date Start date
C
cb9002
I'm buying stuff to run a 4mm2 radial... what depth back box do people suggest? 35mm?
I normally use 25mm ones for ring mains but I'm wondering if I might struggle to get two 4mm2 T+E and a 2.5mm2 T+E in the box behind a DP switch.
(No need to reopen the FCU/DP switch or is a DP switch rated to 32A arguments!)
4mm radial.
2.5mm on the load side of the DP switches run to unswitched undercounter sockets for fridge etc.
errm, 16th I guess, I know nothing about the 17th except the new RCD requirements. What difference does it make? Circuit is RCD protected.
Get those 2.5mm cables replaced with 4mm then, or downrate the protective device to something suitable for the 2.5mm cable (16/20A?)
Ahh, good point thanks, will use FCUs and flex outlet plates instead then.
Seems strange that I could spur from a ring with 2.5mm but not a radial, when both will be protected with a 32A MCB!
The reason I asked is because the 17th allows 2.5 on a 4mm²/32A radial providing it feeds only one outlet.
[Whispers, "Where's FR?" :wink: ]
No need.
Overload protection will be provided by the BS1362 fuse in the plug top. Short circuit protection provided by the 32A MCB.
473-01-02
433.2.2
Securespark - thankyou!
Would I have to make any other changes to ensure 17th ed compliance then? The rest of the house is to the 16th, and the circuit is on the RCD side of a split-load board.
Of course I could just stop being a cheapskate and buy some more 4mm cable...
You have to decide which edition to install it to. You can do 16th OR 17th, but you must not "mix & match"...