Bathroom ceiling build up with cold void above
8 Nov 2024
Hi all,
I'm trying to install a bathroom in an upstairs bedroom. The ceiling is down and i've been trying to think through the buildup of the ceiling but would appreciate a sense check. The room is in the outrigger part of a solid walled semi, so there's an unheated loft space above that isn't used for storage or anything. The membrane has been replaced with a breathable one and there's a good breeze let's say up there. The old ceiling joists are quite twisted and uneven. I've got an extractor fitted up there to vent humidity out of the future bathroom.
The issue is that the ceiling height is not going to be great since we're raising the floor too. So for lighting I was going to try and go with downlights, but I understand that can be a bugger to do with the vapour barrier.
My thinking so far:
- PIR/rigid board between the joists, possibly with rock wool laid perpendicularly on top.
- VCL beneath the PIR flush with the underside of the joists.
- Counter-batten the ceiling from the warm side to level the joists and allow a void for the downlights.
- Moisture resistant plasterboard, either taped and jointed or skimmed.
Presumably those counter-battens need to be 50mm deep to allow for the final plasterboard screws to purchase properly,.... In which case i've eaten into the headroom even more. Most of the downlights that are 'insulation coverable' seem to only be suited to loose insulation rather than rigid board. The ceiling joists are c.100mm deep, do you think i could get away with say fitting the top 50mm with PIR and then using the rest as a ventilation gap for the lighting, somehow stapling the VCL to follow the insulation.
I think your proposed approach is broadly sensible, and you're asking exactly the right questions. However, there are a couple of things I'd change, particularly around the position of the insulation, ventilation and vapour control layer (VCL).
The good news is that I don't think you necessarily need to sacrifice 50mm of ceiling height just to get a decent, level ceiling with recessed lighting.
There is a way of approaching this that should keep the ceiling build-up relatively shallow while still dealing properly with condensation risk.
1. The insulation arrangement
You have approximately 100mm-deep ceiling joists, with a cold, unheated loft above.
My preference would be:
  • PIR insulation between the ceiling joists.
  • Additional insulation above the joists, if the available height and roof ventilation arrangement allow it.
  • A continuous, properly sealed VCL on the warm side of the insulation.
  • A service void beneath the VCL for electrical cables and lighting.
  • Moisture-resistant plasterboard.
One important distinction: any ventilation gap needs to be on the cold side of the insulation, not between the insulation and the plasterboard.
I wouldn't deliberately leave the lower 50mm of your 100mm joists empty as a ventilation channel for the lights. That would put a ventilated space on the warm side of the insulation, which isn't what you're trying to achieve.
2. The VCL and counter-battens​
Your suggested arrangement of putting the VCL beneath the insulation is correct in principle.
I'd arrange it as follows:
  1. PIR between the joists.
  2. VCL running continuously beneath the joists, with all joints taped and sealed around the perimeter and penetrations.
  3. Counter-battens fixed beneath the VCL.
  4. Plasterboard fixed to the counter-battens.
The counter-battens give you a service void, which is particularly useful in a bathroom because you can run electrical cables and accommodate lighting without repeatedly penetrating the VCL.
Do the counter-battens need to be 50mm deep?
No, not necessarily.
You need sufficient timber depth to:
  • Take the plasterboard screws securely.
  • Allow for any unevenness in the existing joists.
  • Provide sufficient clearance for your chosen light fittings.
A 25–38mm-deep batten may be perfectly adequate, depending on the fixing arrangement and lighting specification. You can use packers to level the battens rather than automatically dropping the entire ceiling by 50mm.
3. Downlights – the bit I'd give most thought to​
I agree that recessed lights can complicate things.
There are three approaches worth considering:
Option A – Shallow LED downlights
Look at slim, fire-rated LED downlights with a suitable IP rating for their bathroom location.
Some are designed to fit into relatively shallow ceiling voids. Check their actual installation depth and whether they require clearance from insulation.
Option B – Surface-mounted LED lights
This is probably the easiest solution technically. You retain the full insulation and VCL arrangement, without cutting holes through either.
There are some very neat, low-profile LED fittings available now.
Option C – Downlights within a service void
This is probably the compromise I'd investigate first.
You could create a 38mm service void beneath the VCL and select lights specifically designed to fit within that space.
However, don't assume that a 38mm void automatically accommodates a 38mm fitting. You need to allow for the fitting body, driver, cable connections and any required clearance.
The Insulation Manufacturers Association actually recommends creating a service void beneath insulation to avoid penetrating the insulation and its vapour control layer.
4. Your proposed 50mm PIR / 50mm ventilation gap idea​
I wouldn't do this.
The problem is that the 50mm gap would be below the insulation rather than above it. It wouldn't provide the ventilation needed to protect the cold roof structure.
If you have 100mm joists, I'd be inclined to use as much of that depth as possible for insulation, subject to the roof construction and ventilation requirements.
You could then add further insulation above the joists from the loft side.
For example, a possible arrangement would be:
Illustrative ceiling cross-section
Cold loft – ventilated space
Additional insulation above joists (if appropriate)
Existing 100mm joists with PIR between
Continuous sealed VCL
25–38mm service battens / lighting void
Moisture-resistant plasterboard and finish
Conceptual arrangement, not a construction specification. Insulation thickness and roof ventilation need checking against the actual roof construction.
One important point: the breathable membrane doesn't automatically mean you can disregard roof-space ventilation. Its vapour resistance and certification matter. You need to establish whether the roof is designed as a conventionally ventilated cold roof or a breathable roof construction.
5. A couple of bathroom-specific considerations
Because this is going to be a bathroom, I'd pay particular attention to two things:
  • Extractor: Make sure it actually discharges outside, rather than into the loft. Insulate the duct in the cold loft and arrange it to avoid condensate collecting and running back towards the fan.
  • Air tightness: Bathrooms produce a lot of water vapour. Seal the VCL particularly carefully around the perimeter, cables, pipes and any other penetrations. A good extractor is important, but it doesn't replace a properly constructed ceiling.
Also, have the lighting checked for the relevant bathroom electrical zones and IP requirements.
6. A few things I'd like to clarify​
Having looked at your photograph, I'd like to understand the roof construction a little better before recommending a definitive build-up.
1. Is the new ceiling going to be horizontal or follow the roof slope?
Horizontal ceiling, with loft above
Sloping ceiling following the rafters
A mixture of both
2. Do you know what type of breathable membrane was fitted?
Modern breathable roofing membrane
Traditional bitumen felt
Not sure
3. Are the 100mm timbers definitely the ceiling joists?
Yes, 100mm ceiling joists
They are actually roof rafters
Not sure
4. Can you access the loft above to lay additional insulation?
Yes, easily accessible
Yes, but access is restricted
No
5. Are you committed to recessed downlights?
Yes, definitely want recessed lights
Prefer recessed, but open to alternatives
Happy with surface-mounted lights
Submit answers
My overall feeling: I'd concentrate on getting the insulation and VCL right first, then design the lighting void around them. I wouldn't compromise the thermal or moisture performance of the roof just to accommodate downlights.
With those five details, we can work out a sensible build-up in millimetres and see how much headroom you can realistically save.
Hope that helps.
Thanks, see this is my problem with AI - apart from the unfamiliarity of being complimented, i'm still no wiser as to whether that gap between the back of the plasterboard and the start of the insulation is a bad idea. It seems to refer to it as a ventilation gap, but that's not strictly the intention in respect of the moisture, it's only in terms of the void needed for the downlights and to allow heat to dissipate rather than surrounding it in insulation.
Just don't use recessed lights. There are lots of slim LED lights available these days. I've fitted some that are about 10mm thick, they don't look any different to recessed lights at a glance. It sounds crazy to deliberately make a low ceiling even lower just to sink the lights into, together with all the huge potential issues that arise. Any sealed voids you create are very likely to end up as a great colony of mould, which will then grow out from under the edges of the light fittings.
Recessed lights were a way in the old days of making a big fat light bulb vanish. Those big fat bulbs don't even need to exist now, the need for them and all their complications has gone away.
Hi all,
My thinking so far:
I'm not understanding the need for PIR or counter-battens, when you have loads of room for quilt type insulation. I might be tempted to fix say 50mm foil PIR to the joists first, but that's only because the parts of the ceiling closest to the roof eaves are vulnerable to mould.
Nor do I understand what is stopping that roof from spreading? :oops:
Hi all,
My thinking so far:
I think you're on the right track, especially with planning the insulation and vapor control before closing up the ceiling. One thing I'd be careful about is creating a ventilation gap around the downlights without considering the complete roof and ceiling assembly. Moisture can become a real problem in bathrooms if warm, humid air gets into a cold roof void. I'd also check whether the downlights are suitable for the insulation and required clearances, rather than relying on covers alone. Since you're dealing with limited headroom, it may be worth looking at shallow-rated downlights and a service cavity that doesn't reduce the ceiling height too much. The final insulation and VCL arrangement should follow local building regulations and the roof membrane manufacturer's guidance.
Guessing the top of the visible rafters bear onto a wall, or beam? Possibly.
Don’t really understand why PIR and vcl is being talked about either in this context
Agree with windybum on the downlights
Thanks all. Yes i could do it with rockwool or something but it's only a small space so would only take at most probs 2 boards to do and PIR is just more effective thermal wise.
Have you got any IP65 rated slim LEDs in mind that you'd recommend? I guess anything that isn't surface mounted would need a service void (unless covering in loose insulation), in which case once you introduce the service void and you're fixing into battens then the latter would need to be fairly deep just for the pb to fix into?
Apologies I haven't done anything like this before so might have missed the point, or lots of points!
Is the VCL not quite an important part in stopping humid air getting into the cold space and condensing?
It doesn’t feature in the vast majority of ceilings like this one, as there’s a quilt of insulation separating the room from the cold loft space. But if you want to go belts and braces and a different detail involving one, that’s also fine if you get it right…
It's not belt or braces - a vapour barrier is absolutely essential, especially in a bathroom or kitchen.
If you don't understand why, it's because plasterboard and rockwool are porous. Warm, moist air can penetrate into them, as it moves through the insulation it gets colder and at some point it will reach its dew point and condense out as liquid water and turn the whole lot into a rotten stinking mess.
If it gets through the loft insulation then it will condense onto the inside of the roof, eventually rotting the roof timbers.
If you're going to make wells for lights then these need to be sealed too, which is difficult to achieve. They're usually a cold spot, so a thermal loss and a route into the insulation and structure for the damp.
You need a contiguous impermeable membrane between the room and all insulation. Usually directly behind the plasterboard.
here he goes…
Yes, I know what a vapour barrier is. But remember, the vast majority of non-vaulted ceilings with a loft above, don’t involve one by design and are fine. So to say it’s essential in this case is slightly inaccurate, as long as the loft insulation and ceiling boarding/lighting cutouts are sound.
There are currently 1.2 million 1940's to 1980's built bathroom ceilings, that are not a rotten stinking mess, and not a VB in sight.
Wisdom says fit duplex boards. But then punching (downlight) holes int makes a mockery of the process. A draughty loft is a healthy loft.