OK.... The story so far... " Along time ago in a galaxy far far away" (Not sure if Orpington in Kent counts as a different Galaxy but I'm sure it is not of this world.. MMmmm)
I get asked by a friend of mine to service his back boiler because "It has been over a year since it's last Service" not quite sure why I wasn't asked to service it a year ago, but I suppose it is a free country isn't it..
So I go down there and strip it down and let my Henry hoover and my soft brushes have a field day, and to be honest the sooting on the heat exchanger was awful but I just put it down to the fact that 12 months since it's last service was probably more like 108 months and the poor old thing was just choked up. I cleaned everything thoroughly and then did the standing and working pressure and it was exact 22 mb standing and 11mb working. So I reassembled it all and left with a whole load of sooty dustsheets and looking more like one of the black and white minstrals than Stuart from Surrey.
He calls me today saying the heating is now not working, so off I trundle again and take off the fire and to my dismay the cast iron is in a really bad state again, the soot is all over the heat exchanger.
So gentlemen I need a bit of help with this one..
1... The Standing pressure is fine
2... The working presure is as it should be.
3... The flue liner is pulling a smoke match and pellett with no probs.
4... There is lots of ventilation..
5... The flame does very occasionally appear to be poking it's head over the top of the Heat Exchanger.
I am wondering (Is it possible) that even though the gas valve is sending the right volume of gas to the burner, is it possible that this has some cracks.
It is Friday Night but I would appreciate some help on this one..
Thanks
I get asked by a friend of mine to service his back boiler because "It has been over a year since it's last Service" not quite sure why I wasn't asked to service it a year ago, but I suppose it is a free country isn't it..
So I go down there and strip it down and let my Henry hoover and my soft brushes have a field day, and to be honest the sooting on the heat exchanger was awful but I just put it down to the fact that 12 months since it's last service was probably more like 108 months and the poor old thing was just choked up. I cleaned everything thoroughly and then did the standing and working pressure and it was exact 22 mb standing and 11mb working. So I reassembled it all and left with a whole load of sooty dustsheets and looking more like one of the black and white minstrals than Stuart from Surrey.
He calls me today saying the heating is now not working, so off I trundle again and take off the fire and to my dismay the cast iron is in a really bad state again, the soot is all over the heat exchanger.
So gentlemen I need a bit of help with this one..
1... The Standing pressure is fine
2... The working presure is as it should be.
3... The flue liner is pulling a smoke match and pellett with no probs.
4... There is lots of ventilation..
5... The flame does very occasionally appear to be poking it's head over the top of the Heat Exchanger.
I am wondering (Is it possible) that even though the gas valve is sending the right volume of gas to the burner, is it possible that this has some cracks.
It is Friday Night but I would appreciate some help on this one..
Thanks