baxi duo tec keeps dropping pressure?

Discussion in 'Plumbing and Central Heating' started by Adam78, 12 Apr 2019.

  1. Adam78

    Adam78

    Joined:
    25 Dec 2013
    Messages:
    133
    Thanks Received:
    1
    Location:
    Manchester
    Country:
    United Kingdom
    Hi,

    I have a baxi duo tec 28 HE which keeps dropping pressure and return E119 error code.

    In the last month it's had to be topped up 3 times and I topped up again early this week to 2 bar and today the pressure has dropped to below 1 bar.

    I've checked all the radiator valves for leaks but can't find any. No visible patches on the ceiling either. Downstairs the central heating pipes run under floor boards so can't really check unless I lift all the floors which I really don't want to do.

    Is there any way or test that can be carried out to isolate where the leak is e.g on the boiler or on the system?

    Basically I only want to go down lifting the floorboard if I can be sure the leak is on the system.

    I've checked the pressure release pipe (the copper pipe outside) and no visible signs of water there either.

    Any tips and advice would be appreciated.
     
    Last edited: 12 Apr 2019
  2. Sponsored Links
  3. Odd
     
  4. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,033
    Thanks Received:
    10,115
    Location:
    Livingston
    Country:
    United Kingdom
    I dont believe that Baxi are unwilling to look at it, they will have said that if it isnt boiler related then there will be a charge, not the same thing, why would they not charge if it is nothing to do with them ?
     
  5. Adam78

    Adam78

    Joined:
    25 Dec 2013
    Messages:
    133
    Thanks Received:
    1
    Location:
    Manchester
    Country:
    United Kingdom
    So how would you determine if it's boiler related or not?
     
  6. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,033
    Thanks Received:
    10,115
    Location:
    Livingston
    Country:
    United Kingdom
    there are ways , but as it is a new install , ask your boiler installer to come and confirm that it is definately a boiler problem, why should you be stuck in the middle? get your installer to contact Baxi if the believe it is a boiler fault, they will have a lot more clout than you if they are a genuine installer
     
  7. Adam78

    Adam78

    Joined:
    25 Dec 2013
    Messages:
    133
    Thanks Received:
    1
    Location:
    Manchester
    Country:
    United Kingdom
    It's not a brand new install it's 4 years old and the original installer no longer operates.
     
  8. You could try topping the pressure up and isolate the flow and return under the boiler and leave overnight. If the pressure drops its on the boiler, if it stays the same its on the system.
     
  9. sbgasman

    sbgasman

    Joined:
    7 Apr 2008
    Messages:
    1,692
    Thanks Received:
    780
    Location:
    Yorkshire
    Country:
    United Kingdom
    only needs to be about 1.2 bar cold , tie wrap a balloon over PRV pipe to see if it's passing
     
    • Like Like x 1
  10. Sponsored Links
  11. gasbusters

    gasbusters

    Joined:
    27 Sep 2016
    Messages:
    5,785
    Thanks Received:
    584
    Country:
    United Kingdom
    From cold turn on the heating on high heat and watch the pressure gauge. After 10- 15 mins does it go into the red zone? If so, its the expansion vessel thats either lost its charge or needs replacing. This issue is very common on Baxi and Main combi boilers.

    You say its 4 years old and under warranty? Do you get it serviced every year to ensure warranty is still valid? Recharging vessel is standard in a boiler service.
     
  12. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,033
    Thanks Received:
    10,115
    Location:
    Livingston
    Country:
    United Kingdom
    have you dusted it ?
     
    • Thanks Thanks x 1
    • Like Like x 1
  13. Adam78

    Adam78

    Joined:
    25 Dec 2013
    Messages:
    133
    Thanks Received:
    1
    Location:
    Manchester
    Country:
    United Kingdom
    I checked the pressure relief pipe outside this morning and it did have some water dripping. Yes I do have it serviced annually but the guy doesn't seem to do much when he does the service, he takes some readings and that about it.
     
  14. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,033
    Thanks Received:
    10,115
    Location:
    Livingston
    Country:
    United Kingdom
    your expansion vessel needs pressurising /replaced, supposed to be done during a service but you have been using a poke and go engineer not a proper service
     
    • Like Like x 2
  15. gasbusters

    gasbusters

    Joined:
    27 Sep 2016
    Messages:
    5,785
    Thanks Received:
    584
    Country:
    United Kingdom
    Looks like hes only doing one part of the service.

    He needs to recharge the expansion vessel, shouldnt take him more then 15 mins
     
  16. Adam78

    Adam78

    Joined:
    25 Dec 2013
    Messages:
    133
    Thanks Received:
    1
    Location:
    Manchester
    Country:
    United Kingdom
    Since the boiler is still under warranty would baxi come and fix this as the service is not due for a while?
     
  17. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    24,033
    Thanks Received:
    10,115
    Location:
    Livingston
    Country:
    United Kingdom
    You can try but they might charge you,some manus would just re-charge the vessel if that is all it needs, if the vessel needs replacing they would do that under warranty, sadly in my experience Baxi are not very customer friendly when it comes to warranty calls
     
    • Like Like x 1