lsearson said:
hi
i only just put the mains tester on the garden tap so far which is a very short tee off the kitchen tap and the reading is 4.5bar, which surprises me, if that is the case do i need to do any further testing as if i loose 0.25 bar per floor i should have at least 3 bar on floor 3.
Its a simple fact that a combi relies on the mains water supply for delivering hot water. You need at least 20 li/min open pipe.
If its insufficient then you will have wasted you money on a boiler you cannot use.
If you were paying for all this free professional advice then would you then still want to ignore it?
You dont need a flow cup to measure the flow. Just find a saucepan or bucket of known volume or measure the volume by filling it with a measuring jug. Then measure seconds to fill it.
Just because gas4u is not concerned that does not mean that you should not be either. Remember he is not losing out if YOU find you have wasted £1000 on a boiler you dont have flow rate for!
My mother had a pressure ( static ) of 3 Bar but an open pipe flow of only 4 li/min. It was at the end of about 0.5 kM of 1/2" pipe.
As you have a pressure gauge then measure the flow rate you can achieve with a ( dynamic ) pressure of 1 Bar on your gauge.
Tony