Hi guy's ... yes another newbie with A nest question :sleep:
Searched this but cant find the answer... Installed Nest to my Glow worn betacom 28A and it's all set up but the problem is I think the timer on the boiler, it's not handing over controls to the Nest o_O
Anyone had this issue before?
Edit to say the image attached - the 2x grey wires are going to 2/3
 

Attachments

  • 124170800_10158798252204486_264022859545329444_n.jpg
    124170800_10158798252204486_264022859545329444_n.jpg
    60.2 KB · Views: 171
Sponsored Links
Set timer to constant and see if that helps
 
Removed the 24v link ? you should leave the timer on constant and opening/closing the 24v connection should turn the boiler on and off.
 
Sponsored Links
Have you removed any old wiring? Are you sure you haven’t crossed the black and grey wiring? Have you checked what status the nest is at? Is it connected via wi-fi?
 
The wires you have connected to terminals 1&2 on the heatlink have to be connected between 2&3, 1 is not used on your set up as you have a combi, Also as you are powering the thermostat using T1 &T2 your will have to connect an earth wire to the heat link
 
  • Thanks
Reactions: CBW
The wires you have connected to terminals 1&2 on the heatlink have to be connected between 2&3, 1 is not used on your set up as you have a combi

Yes, should have picked up on this, thank you Ian.
 
Removed the 24v link ? you should leave the timer on constant and opening/closing the 24v connection should turn the boiler on and off.
Only link I can see is in the BUS (ORANGE TAB)

Have you removed any old wiring? Are you sure you haven’t crossed the black and grey wiring? Have you checked what status the nest is at? Is it connected via wi-fi?
Not removed anything, all setup on the stat, wifi connected etc..

The wires you have connected to terminals 1&2 on the heatlink have to be connected between 2&3, 1 is not used on your set up as you have a combi, Also as you are powering the thermostat using T1 &T2 your will have to connect an earth wire to the heat link
I did edit the 1st post, the image shows 1/2 but it is connected to 2/3... I don't have an earth on the heat link! I'll take one from the JB and add that now...
 

Attachments

  • 20201108_133400.jpg
    20201108_133400.jpg
    99.2 KB · Views: 101
  • 20201108_133411.jpg
    20201108_133411.jpg
    115.7 KB · Views: 98
Put the timer on constant and turn off the heating on the nest , does the boiler stop ?
 
Your timer is set on timed not constant, you need to click the little switch to I with the little switch, have you removed the 24V link on the PCB ?
 