Disconnection times......
Immersion - 5s
Lighting - 5s
Exterior lighting - 5s
Boiler - 5s
Doorbell - 5s
Shower - 0.4s
Cooker - 5s (with s/o - 0.4s)
Socket outlets - 0.4s
Agree or disagree??
A shower is fixed equipment, so should it not have 5 seconds disconnection time? (working on the theory that RCD is only a manufacturers recommendation?)
My understanding is anything supplying portable equipment is 0.4s
Fixed equipment 5s
So only question is shower?
Personally, if I was fitting Class 1 lighting outside I would make it 0.4 second disconnection time.
Slight hijack here, but should a dedicated external socket be 0.2 seconds?
As supplementary protection against direct contact using an old BS type RCD (300ms for BSEN), though as far as indirect contact is concerned I'd vote for 0.4s
Ok, I concede the shower. 5s it is.
As for the cooker, I would gice 0.4 if on a CCU & 5 if not.
Dedicated socket 0.2? Well, yes I suppose, but only by virtue of the fact it should be RCD protected.
Having said that, it may be protected by a BSEN 61008/ 61009 device, it which case it would be 0.3.....
hi all
bearing in mind that with mcbs there is no 0.4 and 5s disconnection times- it will happen instantly with the correct amount of current..
i also note that the 17th edition is removing 5 sec disc all together, apart from "distribution circuits"
best wishes
alan
Missed that when I looked at the draft....interesting.
Have noticed however the figures in the EFLI tables are, in the most part, the same whichever table you look at.
hi secure,
dont know how old you are but....
the 5 sec disc is from the 14th edition and earlier..
it was based on "fusing factor"
this was 3 for a rewireable fuse
2.4 for a hrc fuse and
1.5 for an oldie mcb
also note the draft has scrapped table 41C (alternative method) utilizing cpc resistance measurement
Isn't anything in a bathroom 0.4 - So upstairs lights, shower etc?
Everything else 5s, apart from any socket outlets - inc cooker panel if appropriate.
In any case, even if you put everything as 0.4 your fault current is 99% of the time going to the clear the fault within that time anyway.
No. That requirement was removed when the 16th came into force.
As festa says, 0.4 secs for equipment outside with accessible exposed conductive parts.
partpdoctor said:
hi all
there is no such thing as "instant".. it doesn't exist.. everything takes a finite amount of time..
having said that, yes MCB's should trip a lot faster than 0.4s..