No, read what has been written there.ok so both sparkybird and yourself agree that if the circuits are protected by a 30ma rccd then bonding does'nt have to be done
No, read what has been written there.ok so both sparkybird and yourself agree that if the circuits are protected by a 30ma rccd then bonding does'nt have to be done
So where do you think the radiator is going to introduce it from?...liable to introduce a potential...
"If the piping is plastic you do not have to bond them.
If the piping is copper then link all the pipes around the boiler together using earth clamps and 4mm earth cable."
The reg is 413-02-02, it quite clear, unambiguous, doesnt mention bathrooms, kitchens or special locations.
FFS.Thanks , So it says not to run the 4mm bonding wire to the MET but do you bond it to the light circuit or shower or the imersion heater circuit of the bathroom.
i know the barhroom rad should be bonded to the light circuit
And the shower circuit, if there is one.
And possibly the towel rail circuit.
And possibly the grid or sheathing of an underfloor heating circuit.
It is supplementary equipotential bonding, not earthing.
It is there to bond all extraneous-conductive-parts in Zones 1, 2 & 3 to the cpcs of all the circuits supplying Class I and Class II equipment in Zones 1, 2 & 3.
Then I thought you were talking about bathroomsDo you bond a single rad ... .