Boulter (OIL) boiler not firing

For your info;
NORMAL
1. All time controls, thermostats and safety switches made and call for heat.
2. Motor and ignition on (oil and air). Pumping oil and sparking.
3. Solenoid valve opens. (Black object on top of little pump, releases pressurised oil)
4. Oil sprays and is ignited by spark, flame.
5. Photo-cell probe reacts to flame brightness, turns off ignition (spark)
6. Run position.
7. Runs until heating requirement is satisfied via thermostats.

NO FLAME
1. Thermostats call for heat.
2. Motor-fan-pump and ignition on.
3. Solenoid valve opens for oil.
4. No flame?
5. Photo-cell sees no light and reacts
6. Switches motor-ignition-solenoid off.
7. Box at lock out, light on.
8. Sequence can be tried again after lock out time has passed.
 
Sponsored Links
For your info;
NORMAL
1. All time controls, thermostats and safety switches made and call for heat.
2. Motor and ignition on (oil and air). Pumping oil and sparking.
3. Solenoid valve opens. (Black object on top of little pump, releases pressurised oil)
4. Oil sprays and is ignited by spark, flame.
5. Photo-cell probe reacts to flame brightness, turns off ignition (spark)
6. Run position.
7. Runs until heating requirement is satisfied via thermostats.

NO FLAME
1. Thermostats call for heat.


2. Motor-fan-pump and ignition on.
3. Solenoid valve opens for oil.
4. No flame?
5. Photo-cell sees no light and reacts
6. Switches motor-ignition-solenoid off.
7. Box at lock out, light on.
8. Sequence can be tried again after lock out time has passed.

You obviously have no idea how a Riello burner works!!!

I would suggest that you save your comments until until you have something relavent to add to the thread !!
 
Solenoid closes on Riello and spark doesn't happen until ignition phase. If the burner does not attempt ignition burner will circulate oil at wash pressure (solenoid open) without lockout.
 
For your info;
NORMAL
1. All time controls, thermostats and safety switches made and call for heat.
2. Motor and ignition on (oil and air). Pumping oil and sparking.
3. Solenoid valve opens. (Black object on top of little pump, releases pressurised oil)
4. Oil sprays and is ignited by spark, flame.
5. Photo-cell probe reacts to flame brightness, turns off ignition (spark)
6. Run position.
7. Runs until heating requirement is satisfied via thermostats.

NO FLAME
1. Thermostats call for heat.


2. Motor-fan-pump and ignition on.
3. Solenoid valve opens for oil.
4. No flame?
5. Photo-cell sees no light and reacts
6. Switches motor-ignition-solenoid off.
7. Box at lock out, light on.
8. Sequence can be tried again after lock out time has passed.

You obviously have no idea how a Riello burner works!!!

I would suggest that you save your comments until until you have something relavent to add to the thread !!

I was giving general information to the question as they were unsure of the oil burner operation. I did not read that it was Riello. But saying that, I would say you are a bit of a control freak in trying to dismiss other posters comments....take a CHILL pill hot head!
 
Sponsored Links
I thought some control boxes checked the photocell (for dark resistance) in the early stages of the ignition process as a fail safe?

Not an expert on oil burners but have this recollection?
 
Mike2007";p="726170 said:
Terrywookfit";p="726030 said:
Mike2007";p="725829 said:
For your info;



I was giving general information to the question as they were unsure of the oil burner operation. I did not read that it was Riello.

How can it be usefull general information if you have not taken the trouble to read the post, your information was irrelavent!!


But saying that, I would say you are a bit of a control freak in trying to dismiss other posters comments....take a CHILL pill hot head![/quot

How does it make me a " control freak" I only pointed out that you were talking cr*p!!

ps: which manual did you get your information from?? ;)
 
I thought some control boxes checked the photocell (for dark resistance) in the early stages of the ignition process as a fail safe?

Not an expert on oil burners but have this recollection?

Yes they do to ensure there is no flame before oilrelease/ignition!!
 
THanks to you all.

Thought you might like to know the answer. The engineer replaced the phtocell first...no joy. Then he replaced the control unit still no joy. After phoning a few others in the trade it turned out to be the solenoid.

After changing this...hooray....heating again.

He said he had not come across this fault in 15 years, adding that "in this job you're always learning"...so I thought it might be worth passing on.


Thanks again for all you great comments and advice.

Cheers

Peter
 
Terrywookfit";p="726240 said:
Mike2007";p="726170 said:
Terrywookfit";p="726030 said:
For your info;



I was giving general information to the question as they were unsure of the oil burner operation. I did not read that it was Riello.

How can it be usefull general information if you have not taken the trouble to read the post, your information was irrelavent!!


But saying that, I would say you are a bit of a control freak in trying to dismiss other posters comments....take a CHILL pill hot head![/quot

How does it make me a " control freak" I only pointed out that you were talking cr*p!!

ps: which manual did you get your information from?? ;)

You are full of crap mate and let down a good forum. Crawl back under stone you came from! There some top guys on this site and you ain't one of them! ;)
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top