Warning to anybody wanting to upgrade their shower but not the supply to it....
This circuit was originally wired from a BS88 30A fuse on a Wylex Stadard CU, in 4mm² with a 30A pullcord switch, running a 6.5kW shower, then upgraded to 10.5 with no other considerations. The picture is as I found it.
Having looked at the cable, I can see it is heat-damaged: the pvc inner insulation is welded to the outer sheath along its length. The contact to which the live conductor was attached is no longer attached to the CU.