Building regulations and bolting 2 RSJs

Discussion in 'Building Regulations and Planning Permission' started by mk1234, 27 Apr 2011.

  1. mk1234

    mk1234

    Joined:
    27 Apr 2011
    Messages:
    2
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    My question relates to current building regulations for using 2 paralle RSJs.

    The house is victorian with a 27mm wide wall (2 bricks, no cavity). I am knocking through the old exterior wall that now separates the original exterior wall into a newer a kitchen extension.

    If I install 2 178 x 102 x 19 RSJs parallel to each other, will I need to bolt them together? The RSJs will be approx 220 wide when installed.

    I have off-the-shelf padstones for either end of 300 x 215 x 215 and will build out the pier at either end to match the padstone (300mm) wide.

    The RSJs have been purchased already and I do not want to have to drill them unless absolutely necessary, however have been told that new regulations may require them to be bolted together to stop any lateral movement. Has anyone had any experience of this? Will Building Control insist that this is done?

    Many thanks

    Martin
     
  2. Sponsored Links
  3. mk1234

    mk1234

    Joined:
    27 Apr 2011
    Messages:
    2
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    The RSJs are 2850 long if this makes a difference.
     
  4. freddiemercurystwin

    freddiemercurystwin

    Joined:
    21 Jan 2007
    Messages:
    19,866
    Thanks Received:
    2,218
    Location:
    Devon
    Country:
    United Kingdom
    Your structural engineer will advise you.
     
  5. noseall

    noseall

    Joined:
    2 Feb 2006
    Messages:
    43,449
    Thanks Received:
    2,685
    Location:
    Staffordshire
    Country:
    United Kingdom
    I have not installed a pair of steel beams in the last 20 years that were not bolted together.
     
  6. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    33,979
    Thanks Received:
    4,608
    Location:
    West Mids
    Country:
    United Kingdom
    3 nr m10 bolts with mild steel tube spacers at 1/4 of the span will normally do
     
    • Thanks Thanks x 1
  7. DevilDamo

    DevilDamo

    Joined:
    14 Jan 2010
    Messages:
    1,955
    Thanks Received:
    319
    Country:
    United Kingdom
    Your structural calculations "should" also specify this, which is what your BCO would like to see.
     
  8. Static

    Static

    Joined:
    20 Dec 2005
    Messages:
    2,026
    Thanks Received:
    168
    Location:
    East Sussex
    Country:
    United Kingdom
    Its more economical to design the beams as bolted together as independant beams cant span the same distance and twist. If you didnt bolt them together you would probably end up with beams twice the depth.
    As others have said consult your SE, its what your paying him/her for.
     
  9. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  10. Sponsored Links
Loading...

Share This Page