I think I watched the Vaillant engineer going through this sequence. He did give me a rapid verbal update on what he did to back off the boiler but there is no way I could remember that sequence.
Do the bucket test test with the system OFF and from each side in turn roughly measuring how long it takes to say half fill the bucket or any other easy to judge amount.
Its important to start with the boiler pressurised to the same value of say 1.5 Bar. Repressurise after testing the first valve before starting on the second.
The flow in that test is provided by the charge in the expansion vessel and will only run for a few seconds and provide a few litres.
The objective is to see how fast the water comes out at first. There should be a good flow of perhaps 1 litre every five seconds.
Remember at the start there will be 1.5 Bar pressure so the flow can be fairly high.
Agile
Mostly OK. But it's not a system boiler. Just an open vent classic set up. I'll run it with everything off and see what I get.
Any thoughts on the ABV staying hot?
D_Hailsham
I didn't see them actually doing the balancing but at the start they put the caps on (perhaps to stop the flow while taking out the radiators)
I don't think they were cowboys. At least they had a recommendation.
There is always the possibility that a bit of dirt is stopping the valve from closing completely. Unfortunately, the only way of checking this is to remove the valve.
at the start they put the caps on (perhaps to stop the flow while taking out the radiators)
Next test.
Open up 3 rads fully and set room thermostat up.
Back to Boiler and find the flame symbol is alight but it's silent.
d40 says 53c; d41 says 43c
After 2 minutes the traditional boiler sound starts and d40 rises steadily to 67c while d41 still says 43c
Boiler stays at this sound for 4 minutes and d40 67c. eventually d41 rises to 45c.
But this is the first time for ages I've had a steady boiler sound and sustained running
In order to get the boiler working I opened up 3 radiators fully. The bathroom TRV. The hall (that was virtually closed) and the rear bedroom (above the faulty radiator and previously wound down a lot)
All 3 are stonking hot. But the faulty radiator is now warm all over? Not as hot as the others but a very reasonable temperature.
The ABV is still as hot as before so an awful lot of water is passing through it.
And Agile
I'm not ignoring your advice. Just doing the easy stuff first. So far I haven't opened up the loft or got anything wet. I'll be doing that at the weekend.
ps. I'm also very slow (I couldn't make a living from this). The next test is all the radiators off except the poor one. (my wife has just commented on the warmth now in the house but said it's because we have no wind this evening so she's not impressed!)
I had good flow last night. Of the 3 radiators that I put to max I had to turn down the one in the back bedroom (above the faulty one) to reduce the temperature for sleeping.
This morning, the faulty radiator was very cool again.
It seems the boiler was back to short bursts. Opening the bedroom again restored the boiler to longer bursts and then got the faulty radiator running.
More tests tonight. (including everything off except the faulty one)
The flow temperature is probably set to 67C. Is the temperature control on the front of the boiler set to max or something lower?
At 14kW output the max flow rate should be 10 litres/min (0.6m³/hr; 0.17 litres/sec. Depending on which speed you have the pump set to, the head will vary from about 3m to 5m. This is well within the range of your ABV.
Agile
This part of the CH is on one of the only existing bits of pipework. We had the Dining Room/Kitchen knocked through so had to remove a large old panel radiator (to allow the wall to be removed. This new Column Radiator is connected to the shorter pipes. Ironically, this old panel was the warmest in the house. So the relationship of the pipes at the rear of the house is the same with just 2 bedrooms above and this drop coming off the middle of the linking pipes.
I can be fairly confident that there was no linking of performance when it was the original panel.
I shall do the test tonight to see if this new column works with everything else off.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local