Cable diameter for long distance run

Discussion in 'Electrics UK' started by RGi, 11 Oct 2018.

  1. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
    I'm looking to make an extension lead of over 60m to run a well pump of of the generator after storms or other power cuts. It needs to run the pump which is rated at 2400 Watts. What diameter cable is needed for this to allow for power loss over distance.
     
  2. Sponsored Links
  3. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,383
    Thanks Received:
    1,834
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    2.5mm² 3 core flex. 3183TRS or similar.
     
    • Like Like x 1
  4. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
    Thanx! It would be great to know how to work it out so I don't have to ask again?
     
  5. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    3,936
    Thanks Received:
    784
    Location:
    Durham
    Country:
    United Kingdom
    Does the pump not need to run in normal (ie not power cut) circumstances? 2.5mm TRS or SWA would do the job (but SWA isn't exactly an extension cable)- might be better getting one of those cheap site gennies from ebay and not having a 60m cable run
     
    • Like Like x 1
  6. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
    Thanx Oldbutnotdead. The pump runs of a buried sheilded mains, but in outages it runs of a genie and 60 m is the closest it can get.
     
  7. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    3,936
    Thanks Received:
    784
    Location:
    Durham
    Country:
    United Kingdom
    Fair does. For future, you're looking at current carrying capacity of the cable and critically volt drop. This here calculator https://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html will do the basics
     
    • Like Like x 1
  8. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    35,494
    Thanks Received:
    3,971
    Location:
    Retired to:
    Country:
    Portugal
    I can't get TLC's calculator to give a result

    although I can do it manually with a satisfactory resut of 2.5mm² as flameport said.
     
    • Like Like x 1
  9. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,783
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Shouldn't the starting current of the pump be considered?
     
    • Like Like x 1
  10. Sponsored Links
  11. SimonH2

    SimonH2

    Joined:
    4 Nov 2010
    Messages:
    5,707
    Thanks Received:
    579
    Location:
    Cumbria
    Country:
    United Kingdom
    Do you have access to the supply end of the normal power cable for the pump ?
    If so, then you could fit a change over switch there and (say) a BS4343 (aka Commando) power inlet. That would avoid the need to run out a long extension lead every time you need it.
     
    • Like Like x 2
  12. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
    I had a bit of difficulty with it myself. Any chance of the formula or a link to it?
     
  13. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
    I don't know, should it?
     
  14. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
    Good idea but the generator is in a different location unfortunately.
     
  15. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,783
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    What problem(s) were you having?
     
  16. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,783
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Yes, because if it is high in comparison to the steady-state load you use to size the cable the voltage drop when it tries to start my be too high, and it might not start properly.
     
    • Thanks Thanks x 1
  17. RGi

    RGi

    Joined:
    11 Oct 2018
    Messages:
    11
    Thanks Received:
    0
    Location:
    Waterford
    Country:
    Ireland
     
    Last edited: 17 Oct 2018
Loading...