Cable for 12kw electric boiler

What if the boiler was operational on E7 during the night at 26amps (much lower than storage heater circuit). So after this "charging" period of heating if a boost is required it will not exceed the 26amps from a 6kw boiler? Reducing the risk to the supply.
What kind of timed switch could be used for this load?
Let me know what you all think?

That is sounding rather more sensible and cheaper to operate. You may have ti use a time switch/contactor combination to control it.

You need to still apply for the load permission though
 
100A, but the supplier may not allow that sort of load if it affects neighbouring properties.
What if the boiler was operational on E7 during the night at 26amps (much lower than storage heater circuit).
How on earth could one achieve that - if it really is a 'simple' 12kW boiler, then it will inevitably take double that current, no matter what the time of day/night.

As everyone has asked, what exactly is this '12kW boiler', and is there any facility (e.g. multiple switched elements) to run it at less than 12kW ??

Kind Regards, John
 
Domestic property 100amp supply
Aztec boiler
Space heating and hotwater

so it sounds like it is intended to be the permanent heater in the house, no gas boiler, so we can expect it to be running at full power for extended periods, mostly daytime, unless there is a large thermal store and it goes on an overnight economy rate.

This is not a common domestic installation.
 
If you use that type of boiler overnight, your house will be hot at night only. There is no 'charging' as there is nothing to store the heat.

It's also doubtful that a 6kW boiler will be sufficient, unless the house is tiny and exceptionally well insulated with minimal requirements for hot water.

Is there really no option for oil or gas? Either would be substantially cheaper.
 
Or biomass, or air source or ground source heat pumps. Basically anything is cheaper than electricity for heating.
 
Though it does ring a slight alarm bell.

If the OP is considering this it suggests that there is no gas in the area which could be a rural property.
That could raise a question over transformer capacity and what other load is in the area

It isn't all about the size of the individual service
 
...As everyone has asked, what exactly is this '12kW boiler', and is there any facility (e.g. multiple switched elements) to run it at less than 12kW ??
I reckon it's one of these;
http://www.heatandplumb.com/acatalog/Trianco_Aztec_Classic_Electric_Boiler_-_12kW.html[/QUOTE]
You might be right. If so, I have to say that (albeit my experience is very limited) I've never seen or heard of such a device being used in a UK domestic property! Since it talks about linking 6 together to get 72 kW, I somehow doubt that they have domestic usage in mind! Pertinent to this thread, I also note that it says (their colour!!):
Please note - before purchasing any electric appliance we advise you to contact a qualified electrician, who will ensure you have adequate surplus electric supply to run this appliance.

Kind Regards, John
 
Yes, I found that too. There is an error in the docs though. It states the "RCD" value for this device should be 63A.

I rather suspect that should be the MCB value.

SO a nice meaty 16mm² cable from a switch fuse will do it.

re
What if the boiler was operational on E7 during the night at 26amps (much lower than storage heater circuit). So after this "charging" period of heating if a boost is required it will not exceed the 26amps from a 6kw boiler?

As i mentioned above. You really should get an E10 supply.
The structure of the 10 off peak hours is as follows;

3 hours in the afternoon
2 hours in the evening
5 hours over night


Read more: http://www.ukpower.co.uk/home_energy/economy_10#ixzz3Nsb1qqfs E7

The off peak meter arrangement does all the switching, you do not need a separate time switch.

But it will require more than 50AMPS every time it is running.
Ye cannae change the laws of physics, Jim.
 
If the OP is considering this it suggests that there is no gas in the area which could be a rural property. That could raise a question over transformer capacity and what other load is in the area
I have that problem, which is why I have to rely on LPG. Expensive though LPG is, it's a lot cheaper than electric heating would be, even if there were enough supply capacity!

Like others, I'm far from convinced that this 'plan' has been very well thought through!

Kind Regards, John
 
...As everyone has asked, what exactly is this '12kW boiler', and is there any facility (e.g. multiple switched elements) to run it at less than 12kW ??
I reckon it's one of these;
http://www.heatandplumb.com/acatalog/Trianco_Aztec_Classic_Electric_Boiler_-_12kW.html[/QUOTE]
You might be right. If so, I have to say that (albeit my experience is very limited) I've never seen or heard of such a device being used in a UK domestic property! Since it talks about linking 6 together to get 72 kW, I somehow doubt that they have domestic usage in mind! Pertinent to this thread, I also note that it says (their colour!!):
Please note - before purchasing any electric appliance we advise you to contact a qualified electrician, who will ensure you have adequate surplus electric supply to run this appliance.

I have phoned Trianco to ask about it and it is a single phase boiler for domestic use in UK. I have also seen two of them running in small properties locally. The intended house is small with no gas supply.

Kind Regards, John
 
I have phoned Trianco to ask about it and it is a single phase boiler for domestic use in UK. I have also seen two of them running in small properties locally. The intended house is small with no gas supply.
I see. Have you undertaken any estimation of the running costs?

Kind Regards, John
 
I have phoned Trianco to ask about it and it is a single phase boiler for domestic use in UK. I have also seen two of them running in small properties locally. The intended house is small with no gas supply.
I see. Have you undertaken any estimation of the running costs?

Kind Regards, John

Starting the think electric isn't very useful for my needs here?? The place is quite small but old (stone walls) and gas is out of the question (no room for tank). Also oil storage tank would be a site problem, so I turned to electric.

Maybe just a regular E7 storage heater setup would be better?
 
I have a feeling that a large thermal store, on an E10 or comparable tariff, and perhaps solar panels if the roof is large, would make more sense.
 
I see. Have you undertaken any estimation of the running costs?
Starting the think electric isn't very useful for my needs here?? The place is quite small but old (stone walls) and gas is out of the question (no room for tank). Also oil storage tank would be a site problem, so I turned to electric.
Fair enough. If there's not enough space for an LPG tank, have you considered using LPG cylinders? A small neighbouring cottage here has that set-up - with a small bank of large LPG cylinders by the side of the building (with, I think, automated switching between them), and they don't seem to have to be changed very often.
Maybe just a regular E7 storage heater setup would be better?
That's a far more conventional option - and at least it is designed to make use of cheap electricity at night and store the heat for release during the day. I don't really understand how the 'boiler' system is meant to work (other than by using very expensive daytime electricity), since there will presumably be a minimal heat store. As others have said, E10 id probably preferable to E7.

Kind Regards, John
 