I was more critical of putting storage heaters on the ring and overloading. If someone can't afford to fit ch they may start to buy storage heaters one at a time, so where do they stop? Do they fit 1,2,3 or 4? They are not expensive, relatively maintenance free and easy to fit on the ring as you suggest. I don't have a copy of wiring regs, but I thought the recommendation was that immersion heaters and permanently connected heating appliances forming part of a comprehensive heating system should be on separate circuits and not connected to the ring. I thought the usual method of wiring storage heaters was on radial circuits which are each designed for a maximum load of 3.4kW both for current capacity and voltage drop. That means for most houses a 2.5mm² radial circuit, up to about 30m, would be ok. If each circuit is designed for the 3.4kW load then a 20A switch with flex cord outlet is needed and not a plug and socket. This allows for upgrading to the 3.4kW heater without any changes to the circuit. I've got a separate CU for my off-peak demands which is 8 storage heaters and an immersion element. I really think this is the way to wire this stuff but I'm only diy, and may have been wrong on my views of earthing metal capping for cables outside permitted zones, so I'm here to learn if I'm wrong. (I thought you were a pro plugwash?)