Cable question, Vent-Axia extractor fan
24 May 2007
In the manual it says. The cross - sectional area of supply cord used should be ranged from 1 -1.5mm2. The extraction fan is suitable for connection to 220-240V 50Hz supply.
My question is, I have some 2 x 0.75mm that is rated at 6 Amps. Would this be OK to use?
I am plugging it into a socket on the wall. 5m run and the cable will be fixed. I am confused to why they say use 1 - 1.5mm on a small 13l/s fan.
Does it say anything about the starting current?
Are the terminals in the fan designed to accept small stranded conductors?
That is so, so horrible.
Perhaps they expect it to be connected to the installation wiring, not plugged in.
If your product draws less than 6A and subject to any derating factors, whilst it may seem OK from a current rating, maybe 1 -1.5mm2 is the size of cable that the fan terminals are designed to accommodate, so wire of a smaller csa may not be clamped adequately. Also, Vent-Axia may be taking into account mechanical considerations, such as strength, vibration etc., Generally if the manufacturer makes a recommendation it's usually best to consider it.
You could of course ask their technical helpline Tel: 0344 8560594. If you do, it would be good to hear back from you what they say.
After what you have said, I'm now going to spur off the socket into a fused 3A switch and then run a 1.5mm twin and earth from there to the fan. Is this acceptable?
I have some grey 1.5mm in the garage so I will use that and went out yesterday and bought some proper trunking to do the cable properly. I was trying to take the cheapest way out. I realise now that is not the best policy.
Thanks all for your advice.