Discussion in 'Plumbing and Central Heating' started by Schimmy, 20 Apr 2018.

  1. Schimmy

    Schimmy

    Joined:
    20 Apr 2018
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    As it’s now summer I’ve wanted to switch off my heating entirely. It’s a modern system in a new build house. I’ve got a control panel (that now shows heating as off, hot water still on fine). I noticed that some of my radiators were still hot - even though on their controls I had turned each down to 0.

    I then took a look at the boiler and it shows a heating symbol, so I switched the heating aspect of this off too. This then meant that the radiators were cold - great! BUT, I then took a shower the next day to find I had no hot water (tab water was still hot), I guess this comes from a tank in the airing cupboard. So, I then turned the boiler back on but am back with two radiators that are slightly warm.

    I’ve got two switches (look like light switches) in the airing cupboard, I don’t know what either do (guess one is the immersion) but the highest one is turned on.

    The tank in there makes intermittent noises, a 5-10 dull mechanical whining sound, followed by a higher pinched ‘climax’ type sound.

    I have no idea how the heating system works and none of the instructions I have seem to work. Any help is much appreciated!
     
  2. 75pete

    75pete

    Joined:
    9 Apr 2008
    Messages:
    661
    Thanks Received:
    60
    Location:
    London
    Country:
    United Kingdom
    So let's start by asking the make and model of the boiler
    Can you post a picture of said parts
    Are the two rads in bathrooms
     
  3. Sponsored Links
  4. Schimmy

    Schimmy

    Joined:
    20 Apr 2018
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi, images attached.

    The radiators are at the bottom of the stairs and also in the living room (open plan with kitchen boiler in same room)

    Thanks!
     

    Attached Files:

  5. BWC

    BWC

    Joined:
    22 Apr 2018
    Messages:
    72
    Thanks Received:
    6
    Country:
    United Kingdom
    Ok ... mmmm
    Need more information really , first thing I’d be looking at with no demand for heating at the programmer and room stat is to check that the 2 port valve (white box) which will have a silver leaver on the side is not locked open, leaver should be under resistance and not floppy when closed , danfoss 2 port valves which you have can keep the boiler to run and override external controls if they stick in the open position due to a seized valve spindle or stuck in its manual override position, you could also try with water only selected at the programmer feeling the pipe that exits the heating 2 port valve for let by. Post back with what you find ...

    Cheers
     
  6. Sponsored Links
  7. BWC

    BWC

    Joined:
    22 Apr 2018
    Messages:
    72
    Thanks Received:
    6
    Country:
    United Kingdom
    Should of said to establish what valve is controlling your heating establish which valve has a pipe connecting to the hot water cylinder , this will be the the hot water 2 port , the other one will be the heating 2 port this is the one that needs checking out.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page