Ceiling Light Blowing Bulbs

Joined
30 Mar 2021
Messages
450
Reaction score
72
Location
Glasgow
Country
United Kingdom
I installed a 5 bulb ceiling light in my living room, the electrics are pretty old with black and red wires in the cables throughout it seems, the cable to the ceiling light doesn’t have an earth wire.

https://www2.next.co.uk/style/st366399/301626#301626

The connector for the light was those little plastic plug connectors, so I wired live to live and neutral to neutral, plugged it in and it switched on fine even though I really should have an earth wire for the metal casing.

I used the recommended LED candle bulbs from Next and by the end of the night one had already blown... few days later another had gone and now tonight another.

What’s the most like cause of this?
 
Sponsored Links
Cheap bulbs
or
Loose connections
are the usual causes of bulbs blowing before their time.
 
If the light fitting does require an earth connection, and you don't have an earth connection, why would you fit it?
 
Sponsored Links
The bulbs could be making poor contact in the lamp holders.

Ah OK, they’re the SES screw in type... I need to pick up a pack of two I had ordered to replace the blown ones .... I’ll check them for tightness in the holder when I replace these.

If you have a 5 bulb light and only 4/5 or working, can this affect the remaining bulbs or would it not matter?
 
Some LED lamps have been found to be easily "blown" by over voltage spikes on the mains. These spikes can be caused by motors ( fridge compressors, tools etc etc ) being turned on and off.

A spike suppressor fitted close to lamp(s) may reduce the failure rate,
 
Choose a Class 2 light fitting which doesn't require an earth connection - very common now
or
Adapt the ceiling wiring so there is an earth on all or part of the lighting circuit.

For the 2nd option there (since I’ve already purchase the light and like it) what would need to be done to a achieve this?

Im assuming every ceiling light on the property has the same issue.
 
For the 2nd option there (since I’ve already purchase the light and like it) what would need to be done to a achieve this?

Im assuming every ceiling light on the property has the same issue.

Firstly, are you SURE there are no earth wires?

Sometimes folk stuff the earth wires in the ceiling void.

(If your wiring happens to be in metal tube, this is the earth.)
 
1. You can only use class II equipment with pre-1966 lighting installations without an earth, but this will not cause bulbs to fail.
2. LED bulbs can be affected with spikes on the supply, having a surge protection device (SPD) will likely reduce bulb failures.
3. Bulb price does not relate to bulb quality, so expensive bulbs will not help.
4. Any switch of bad connection can cause spikes, so @sparkwright comment on poor connections is good.
5. Often dimming switches can either produce spikes or remove spikes, as with any electronic switch.

I have moved to LED in both last house and this house for most of my lights, and can count the failures, even when going back 5 years or more since so few, I had so poundworld G5.3 0.58 watt MR16 lamps fail, they were really toys, I had a 5 foot replacement for a fluorescent fitting fail, rather annoying as not cheap, and a G9 bulb failed, and I decided to set what was inside it, found a dry joint which I corrected, and it is now working again.

I would guess around 35 LED bulbs in this house, may be more, been in this house around 2 years, the houses before also used LED and no fails other than listed above, so the big question is why do I have no problem and I use cheap bulbs, and others have problems, I can only guess, and my guess is because this house has a SPD fitted and non of the houses were near an industrial area or supplied with over head power lines from local transformer, so unlikely to have any spikes on the supply large enough to cause the LED to fail.

I have had problems with LED, but not failing these two G9-comp.jpg LED's are both G9 fitting, the large one has a smoothing capacitor inside nearly as big as the small one, so the small one flashed when switched off until a load capacitor was fitted, then shimmered when switched on, it was a well known make and complied with all regulations, and the glass cover would still fit when using the small LED. The large LED no flicker, brighter, did have one which had a dry joint it failed within a day, and repaired, they were cheap, no brand name breaks the rules by not showing wattage or lumen output, but work far better than the expensive smaller one.

I have had problems with smart switches, and have started to move to smart bulbs, to date the smart bulbs (zigbee) have been better, except for one event, I had four smart bulbs and smart switch in my bedroom, and I turned down the smart bulbs so as not to attract flying insects at night, and the wattage dropped below the minimum for the smart switch so all lights turned off, fitting non smart bulbs did not allow me to switch lights back on, and I had to switch off at consumer unit and back on again to get smart switch to work again.

But smart switches and dimmer switches do seem to stop the spikes with cause bulbs both tungsten and LED to fail, but unless one fitted an oscilloscope to the supply it would be hard to say what causes LED bulbs to fail, I in the main use Lidi, B&M bargains, and Home bargains to buy bulbs, i.e. cheap ones, the only exception was the replacement for fluorescent tube was screwfix (and first one failed) and the G9 which do not comply due to not being marked with watts or lumen came from internet.

So I would say you have been very unlucky.

The non earth problem is some thing else, had it with parents house, and also found wired with rubber insulated cables, the rubber was well past use by date, and my father said "I am not living in a building site, you can re-wire the house when I'm gone." and that is what happened, RCD's would not hold in with the old wiring and it was clearly in a dangerous condition, so when late mother went into hospital we hired a firm to rewire the house, speed was critical as would cost around £600 a week for mothers care if not completed on time, so went with a large firm who could complete fast.

I had only a basic re-wire no extras, and kitchen had already been rewired, seem to remember cost around £2500, and I did the re-decoration plastering etc. As said very basic re-wire, I wanted it safe for mother and able to rent the house if she went into a home. So no frills.
 
For the 2nd option there (since I’ve already purchase the light and like it) what would need to be done to a achieve this?

Im assuming every ceiling light on the property has the same issue.
To run an earth wire would take as much effort as to run twin and earth in most cases, so looking at a re-wire.

I had a hard time finding a light for parents house marked as class II, and it cost twice the price as one which looked identical from B&Q which did not have the class II sticker, so do wonder if the firm specialising in class II lights simply stuck on class II stickers.

My parents years ago got a fluorescent fitting (4 foot) with a BA22d connector that simply plugged in to replace the bulb, however I could not find any fluorescent fitting which was classed as class II except for the folded fluorescent called 2D.

Class II does not mean no metal, some lights have nylon tubes inside the chrome tubes to from a reinforced insulation and are still classed as class II as a result, but to safely use the existing fitting likely means a step down transformer and extra low voltage bulbs (12 volt).
 
1. You can only use class II equipment with pre-1966 lighting installations without an earth, but this will not cause bulbs to fail.
2. LED bulbs can be affected with spikes on the supply, having a surge protection device (SPD) will likely reduce bulb failures.
3. Bulb price does not relate to bulb quality, so expensive bulbs will not help.
4. Any switch of bad connection can cause spikes, so @sparkwright comment on poor connections is good.
5. Often dimming switches can either produce spikes or remove spikes, as with any electronic switch.

I have moved to LED in both last house and this house for most of my lights, and can count the failures, even when going back 5 years or more since so few, I had so poundworld G5.3 0.58 watt MR16 lamps fail, they were really toys, I had a 5 foot replacement for a fluorescent fitting fail, rather annoying as not cheap, and a G9 bulb failed, and I decided to set what was inside it, found a dry joint which I corrected, and it is now working again.

I would guess around 35 LED bulbs in this house, may be more, been in this house around 2 years, the houses before also used LED and no fails other than listed above, so the big question is why do I have no problem and I use cheap bulbs, and others have problems, I can only guess, and my guess is because this house has a SPD fitted and non of the houses were near an industrial area or supplied with over head power lines from local transformer, so unlikely to have any spikes on the supply large enough to cause the LED to fail.

I have had problems with LED, but not failing these two View attachment 241588 LED's are both G9 fitting, the large one has a smoothing capacitor inside nearly as big as the small one, so the small one flashed when switched off until a load capacitor was fitted, then shimmered when switched on, it was a well known make and complied with all regulations, and the glass cover would still fit when using the small LED. The large LED no flicker, brighter, did have one which had a dry joint it failed within a day, and repaired, they were cheap, no brand name breaks the rules by not showing wattage or lumen output, but work far better than the expensive smaller one.

I have had problems with smart switches, and have started to move to smart bulbs, to date the smart bulbs (zigbee) have been better, except for one event, I had four smart bulbs and smart switch in my bedroom, and I turned down the smart bulbs so as not to attract flying insects at night, and the wattage dropped below the minimum for the smart switch so all lights turned off, fitting non smart bulbs did not allow me to switch lights back on, and I had to switch off at consumer unit and back on again to get smart switch to work again.

But smart switches and dimmer switches do seem to stop the spikes with cause bulbs both tungsten and LED to fail, but unless one fitted an oscilloscope to the supply it would be hard to say what causes LED bulbs to fail, I in the main use Lidi, B&M bargains, and Home bargains to buy bulbs, i.e. cheap ones, the only exception was the replacement for fluorescent tube was screwfix (and first one failed) and the G9 which do not comply due to not being marked with watts or lumen came from internet.

So I would say you have been very unlucky.

The non earth problem is some thing else, had it with parents house, and also found wired with rubber insulated cables, the rubber was well past use by date, and my father said "I am not living in a building site, you can re-wire the house when I'm gone." and that is what happened, RCD's would not hold in with the old wiring and it was clearly in a dangerous condition, so when late mother went into hospital we hired a firm to rewire the house, speed was critical as would cost around £600 a week for mothers care if not completed on time, so went with a large firm who could complete fast.

I had only a basic re-wire no extras, and kitchen had already been rewired, seem to remember cost around £2500, and I did the re-decoration plastering etc. As said very basic re-wire, I wanted it safe for mother and able to rent the house if she went into a home. So no frills.

I actually replaced the switch at the wall myself for a new unit well a good few weeks before I replaced the ceiling light ... just a Click Mode on/off switch but as you can no doubt tell, I’m no electrician.

I wonder then if it’s the switch that is the issue.

Im pretty certain there was no earth wire in the grey PVC cable that runs to the ceiling but I may have another look and just make sure it wasn’t snipped right back to the PVC sheath and hidden. There doesn’t seem to be any metal pipe or conduit which the cable runs through.

A rewire here is out of the question at the moment if it’s significant in terms of cost or upheaval.
 
Ah OK, they’re the SES screw in type... I need to pick up a pack of two I had ordered to replace the blown ones .... I’ll check them for tightness in the holder when I replace these.
I have found that it is often caused by the spring contact for the middle connection being too slack. Bending it forward would be the cure. With the power off at the Consumer Unit of course.
 