Central Heating pump

classic plumber line trying to condemn a bulletproof kingfisher boiler mate, don't let them mug you off for a full swap if the cast iron heat exchanger is fine. for those 30 year old 1 1/2 inch pump nuts, soak them in plusgas for an hour then get a blowtorch on the iron nut while holding the pipe with a decent footprint wrench so you don't twist the copper. if they're completely fused, the proper trick is just buying a grundfos ups3 or similar pump head, unbolting the 4 allen bolts on the pump face, and leaving the existing iron pump body in the pipework so you don't even have to crack the unions.

Last Friday, in a kinda 'panic' mode, had a local plumber come around and virtually condemned the boiler. One of his solutions was to remove one rad and replace with a smaller one as a temp fix and join the pipe to the rad with a pump.

Also told me all about having to drill holes in the ceiling which may be Artex, etc. and would have to get an asbestos report before they could do anything. And as access to the boiler was so restricted, it would have to be pulled from the cupboard to replace the pump. The bad news just continued to get worse. Received his quote today for a complete boiler replacement, £8.5k

But having removed all the panels and vacuumed X years of dust bunnies, I can see that access to the pump nuts is not a big deal and certainly will not involve removing the boiler. So he has quoted himself out of a job.

Many thanks for all the advice and I will get a completion photo when the job is done.

I do know that the Corgi pump is not the highest quality but my good friend, Mr A. Intelligence tells me that I can expect up to 10 years of light, domestic use. By that time, I will be in my 80ies and most likely planning to sell the place. So I'll take my chances!!!
 
Also told me all about having to drill holes in the ceiling which may be Artex, etc. and would have to get an asbestos report before they could do anything.
Just on that, that is the correct advice. Cheaper just to get a local sample done.
 
Cross Thread; that is a valid point. Don't think it will be an issue as the piping from the rear of the pump (and rear valve) will have sufficient flexibility with a number of bends, etc.
 
I do know that the Corgi pump is not the highest quality but my good friend, Mr A. Intelligence tells me that I can expect up to 10 years of light, domestic use. By that time, I will be in my 80ies and most likely planning to sell the place. So I'll take my chances!!!
If it costs you nothing to make these mods, why not spend a extra say £50 or £60 and get a really decent pump like a DAB Evosta 3.
 
Started first page, kingfisher and gravity was enough plus no heat.

This is what I would do
1. Check if pump getting 240 volts when heat is calling. HW demand does not run the pump.
2. Find a stick that will starve as a stethoscope, one end on pump and other to ear a jammed pump will emit a hum, a pump that runs will create a water flowing in a stream noise.
3. If pump goosed, look at existing pump or body and locate directional arrow indicating flow of water as new pump will need fitting the same way
4. Get the following (search is from toolstation)
IMG_1396.jpeg
IMG_1397.jpeg
IMG_1398.jpeg


5,In the loft you will find a small 4 gallon water cistern. Plug one rubber bung into the outlet from the cistern ( most likely 15mm pipe) and other mouth of the pipe that rises and loops back towards the cistern
6. Now using a spanner that fits well onto the pump valves, close both valves working the spindle back and forth to achieve best isolation possible. Open drain cock and let the pressure out. You will not be draining the system but creating a vacuum in the system. Close drain valve.
7 now you can mount an assault on the pump but make sure only one pipe is open at any timer or you will wonder where all the water is coming from. 1.5” capnut can be shocked to break the bind, cut even, copper pipe can be cut at accessible position, pipe capped and the other pipe cut.
8 easier to get pro in who does not want to sell you a new boiler
9 come back here for guidance on how you can achieve savings on gas consumption from existing system by tweaking and additional controls

Ps not edited text
 
Thanks for the heads-up. Not totally necessary but I will drain the loft tank first, if for no other reason than to clean all the gunk from the bottom.

Only about third full so not a lot of water. Don't intend to replace the gate valves but I do have a new pair if necessary and at best, can replace a cut flange nut.

As for getting a plumber, those I have called are fully booked or have a bankrupting emergency call-out fee. Fair enough, everyone has to make a living and most of the call-out would probably be transportation to site.
 
Thanks for the heads-up. Not totally necessary but I will drain the loft tank first, if for no other reason than to clean all the gunk from the bottom.

Only about third full so not a lot of water. Don't intend to replace the gate valves but I do have a new pair if necessary and at best, can replace a cut flange nut.

As for getting a plumber, those I have called are fully booked or have a bankrupting emergency call-out fee. Fair enough, everyone has to make a living and most of the call-out would probably be transportation to site.
Can see things going belly up but carry on fella, I wish you good luck.

They say fools rush in where angels fear to thread

Not calling you fool but your statement above has bid potholes in it
 
If it costs you nothing to make these mods, why not spend a extra say £50 or £60 and get a really decent pump like a DAB Evosta 3.
Totally agree our go to pump well made easy to adjust yet to have one go wrong.
Dab totally owned by Grundfos but a much better pump.
Recently spoke to technical manager at Grant re sending back several failed Grundfos pumps.
Grant fitted Grundfos pumps for less than a year.
Was told failure rate was around 1 in 4
At one point Grant had 1.3 million pounds out in warranty claims to Grundfos.
 
Totally agree our go to pump well made easy to adjust yet to have one go wrong.
Dab totally owned by Grundfos but a much better pump.
Maybe I was unlucky, but disagree at this point. Had a Dab fitted in my house for less than 2 years iirc, and it had failed. Grundfos currently in and wouldn’t touch Wilo with a barge pole.
 
Strange what's happened to Grundfos. I've had UPS 15-50 and UPS 2, which have been fine, for years I would only have Grundfos as I thought worth extra ££ for the quality. But I wouldn't have a UPS 3 or later, overcomplicated and I've heard unreliable. Sounds like DAB if I ever need another.
First I've heard bad things about Wilo.
 
For info, there are 18 UPM3s in four houses on our small development. No failures in 5.5 years since houses built early 2021.

I know as I'm the resident DIYer/heating controls expert etc etc for the neighbours.
 
4 or 5 pumps per house? What are they doing?
In each house, one for ASHP flow, another main UFH flow to manifolds then one per UFH manifold on each floor of house so 4 in the two storey houses, 5 in the three storey houses.

Houses c 2,600 sq ft.

Plus one each Stuart Turner 15/60 for DHW circ in our 3 pipe systems. One of them failed in neighbours house recently who had no idea plumber had left it on 24/7 for 5 years. Even the new plumber who came to replace it didn't suggest to neighbours the controller didn't need to be calling for this pump to be on all the time.

They had been using immersion heater twice a day as the ASHP couldn't satisfy the DHW cylinder which the plumber had also left the stat set to 65C when ASHP was set to 48C for DHW demand.

Original installing plumbers had never installed ASHPs before and went bust shortly after build complete as developer never paid them (he has form in the area).
 
For info, there are 18 UPM3s in four houses on our small development. No failures in 5.5 years since houses built early 2021.

I know as I'm the resident DIYer/heating controls expert etc etc for the neighbours.
Newish clean systems.

While obviously all heating systems should be clean in real life not always the case.
The ups 3's seem very prone to stopping. I've seen the 'deblocking' screw leak after use.
When the screw won't push in Grundfos technical answer is hit the screwdriver with a hammer!
 