In each house, one for ASHP flow, another main UFH flow to manifolds then one per UFH manifold on each floor of house so 4 in the two storey houses, 5 in the three storey houses.
The plumbers installed 12 heating zones in all four of the 4 bed houses and fitted 12 Heatmiser NeoAir thermostats each requiring independant programming. They fitted the bathroom floor stats (set to air reading) on the walls outside of each bathroom.
As the manifold is controlled by a UH8 wifi unit, I swapped all my stats to the NeoStat version which can be controlled via their app, has blanket profiles, copy and paste etc. A whole lot easier than running around the house every time I went away for a week.
Consensus is not to zone the Samsung ASHP but to run it in water law (weather compensation) and leave all zones open on low and slow heating. As mentioned, the plumbers had never done an ASHP install before and it took some time to get Samsung to issue the warranty document. To add to their workload, they installed Viessman for two houses and Samsung for the other two and I've discovered they have two different operating philosophies. Viessman installs using W Plan with the three port at rest in heating mode and the Samsungs on S Plans.
As mentioned on another thread, plumbers wired 13A fused spur to Samsung controller using 1.5mm flex not realising the controller needed 13A once a week to run the immersion on it's Legionnaires cycle.
Now I've tweaked stats, flow valves etc, we use c 8,000 KWHr a year whereas our neighbours are consuming upwards of 13,500 KWHr/year for similar lifestyle/usage.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local