    Hello

    I currently have a consumer unit without any rcd's. It just has main switch and mcb's. I believe that I need rcd protection for at least the downstairs sockets, is this correct? Is there any other circuits that need RCD protection? Would I be able to use rcbo's instead of RCD's for the protect and meet the necessary regulations? Thanks.
     
  2. Sponsored Links
  3. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    35,476
    Thanks Received:
    1,150
    Country:
    United Kingdom
    Under the previous regs, socket outlets likely to be used to supply equipment for use outdoors required RCD protection.

    Under the current regs, all circuits require RCD protection. If your board has RCBO's available for it, then they could be substituted. However, it is reportable work & an EIC should be produced too.
     
  4. Hugo329

    Hugo329

    Joined:
    18 May 2009
    Messages:
    12
    Thanks Received:
    0
    Location:
    Lincolnshire
    Country:
    United Kingdom
    What would be the best way to do this then as getting an RCBO for each circuit would be quite expensive, are there more cost effective ways?
     
  5. kevindgas

    kevindgas

    Joined:
    28 Mar 2006
    Messages:
    5,743
    Thanks Received:
    479
    Location:
    Hedge End Hants
    Country:
    United Kingdom
    probably going to be cheaper in the long run to replace the board than fit RCBO's throughout, as the test required is virtually the same
     
  6. Chri5

    Chri5

    Joined:
    19 Jan 2007
    Messages:
    4,289
    Thanks Received:
    391
    Location:
    London
    Country:
    United Kingdom
    Dual RCD board would run to £140 + labour for a 10 circuit board with 10 x MCB's- say a days labour with full tests and paperwork write up.

    RCBO's range from £25-£40 each, but are a 5 minute per circuit job + the testing.

    RCBO's fit the requirement far better since they disconnect the same as an RCD but have only the fault circuit rather than a group of circuits on them.

    Far less inconvenient for the user and by far the best way to comply with 17th requirements.
     
  7. ColJack

    ColJack

    Joined:
    16 Feb 2007
    Messages:
    11,793
    Thanks Received:
    409
    Location:
    West Midlands
    Country:
    United Kingdom
    depending on the board you already have you might be able to split it up and fit rcd's to it to make it a split load board..
     
  8. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    16,795
    Thanks Received:
    1,528
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    As with many electrical jobs there are many ways to comply with the regulations. However often by time one includes labour, materials, and LABC charges non are cheap.

    So lets compare the single unit width RCBO with the multi-circuit RCD.
    1) RCBO only switch the line which with a TN-C-S supply is fine but there are issues with a TT supply.
    2) Using the same RCD for safety circuits and power circuits can present dangers and a risk assessment is really required to work out the likely hood and results should a RCD trip. Although it is considered that in the main if the sockets are not in same area as lights protected by a RCD it is OK. This is not always the case.
    3) Auto resetting RCD's are very expensive around £250 and are not normally used in domestic installations.
    4) Emergency lights are also expensive but there are some cheap options including re-chargeable torches which will light on power failure but the use of these in domestic is also in debate as the home owner can so easy disable the safety item without realizing what his actions could mean.
    5) The use of Ali-tube cable and RCD sockets or Plugs is also subject to control problems and all too easy to be unintentionally disabled.
    6) Mini consumer units although may be considered in same way as FCU's are rather uncertain as to if Part P covers them or not and as such hard to advise as to their use.

    I is hard therefore to give any hard and fast advice on which way to proceed and only with a site visit can anyone advise as to best way forward. If there was no Part P I would change my duel RCD system for RCBO's but cost v advantage does not warrant change. However if I did not already have duel RCD I would fit RCBO
     
  9. Hugo329

    Hugo329

    Joined:
    18 May 2009
    Messages:
    12
    Thanks Received:
    0
    Location:
    Lincolnshire
    Country:
    United Kingdom
    Thanks for all you comments.

    So you say that all circuits needs RCD protection now, is that lighting, shower, sockets, everything?

    The CU that is installed is a Volex one, do you know if it is possible to change these in splitload units?
     
  10. Sponsored Links
  11. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    67,825
    Thanks Received:
    3,712
    Location:
    Coastal
    Country:
    Cook Islands
    the rules have changed for new installations, so if you were building a new house you would be unlikely to have any circuits that did not have to go on an RCD

    However an old house is not obliged to be rewired every time the rules change.

    For safety, I would say at least the shower and sockets should be RCD protected.

    How many circuits do you have, and how old is your consumer unit?

    RCBOs are coming down in price as they get more popular.
     
  12. Hugo329

    Hugo329

    Joined:
    18 May 2009
    Messages:
    12
    Thanks Received:
    0
    Location:
    Lincolnshire
    Country:
    United Kingdom
    I have 7 circuits:-

    upstairs sockets
    downstairs sockets
    upstairs lights
    downstairs lights
    cooker
    shower
    garage (with goes to a garage cu)

    the cu was installed about 5 years ago
     
  13. Hugo329

    Hugo329

    Joined:
    18 May 2009
    Messages:
    12
    Thanks Received:
    0
    Location:
    Lincolnshire
    Country:
    United Kingdom
    I'll correct that last posting actually

    I have 9 circuits:-

    upstairs sockets
    downstairs sockets
    upstairs lights
    downstairs lights
    central heating controller
    extra sockets on a radial
    cooker
    shower
    garage (which goes to a garage cu that is RCD'd)

    the cu was installed about 5 years ago
     
  14. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom

    [​IMG]

    .
    .
    .
     
  15. electronicsuk

    electronicsuk

    Joined:
    7 May 2007
    Messages:
    3,316
    Thanks Received:
    275
    Location:
    Lincolnshire
    Country:
    United Kingdom
    Are you sure the main switch isn't an RCD? An installation of that age should have had an RCD installed on the downstairs sockets as a minimum.
     
  16. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,757
    Thanks Received:
    2,019
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Hugo, I recently spent a horrible time putting in just two RCBOs into a Volex board. What should have taken 30 minutes took half a day.

    The Volex board is, in my opinion, not designed to accomodate RCBOs, there's no head room and the existing main connect cables and busbars make it an almost impossible job.

    If it were my decision, I'd bite the bullet and get a nice new QUALITY 17th edition consumer unit installed.
     
  17. Hugo329

    Hugo329

    Joined:
    18 May 2009
    Messages:
    12
    Thanks Received:
    0
    Location:
    Lincolnshire
    Country:
    United Kingdom
    Thanks for the info on the Volex board.

    Yes the main switch is just a main switch. I bought the house about 4 1/2 years ago and they said it had just been rewired.

    Is it possible to add RCD's to the board and what sort of rating would I need? Would it have to be a split load with 2 RCD's or can it be done with just 1?
     