I moved in to my house, a 3 bed linked detached in 2002, and we had the kitchen revamped. The previous owner had two heating units in the kitchen, one for the central heating, another under the sink for instantaneous hot water by gas. (The house originally was heated by warm air). In place of two units the designer’s agent installed a combi boiler for which here are some details.
Protherm 80e
Flow rate @ 30 deg C temperature rise ….11.2 l/min
@35…………………………… 9.6 l/min
Minimum water flow……………………….2 l/min
Max/min supply pressure……………………6/1 bar
Full technical details are at
http://www.postimage.org/image.php?v=gx1mujcr
The boiler has never seemed particularly good on the DHW side, and that applies especially to running a hot bath and various things have neen done to make matters more satisfactory
10/11/05 replaced air in expansion vessel
28/11/05 replaced faulty plated
15/12/06 service note “pressure vessel may require recharging, not very good”.
12/02/07 re-pressurised expansion vessel, cleaned prv
18/02/08 replaced DHW diaphragm.
None has been particularly effective. We can only run a bath at a very slow rate, no more than a 10 deg twist f the taps beyond which water runs hot and cold.
We recently consulted a local engineer, who suggested that a power flush (£450) might be the solution, but also that the boiler was likely inadequate for us.
We are the two occupants and as well as DHW the boiler serves
2x26" double radiators; 2x33" doubles; 1x63" single; 1x44" single;
1x26" low level that goes under kitchen breakfast corner. double will grille on top; hated towel airer 600x1150 mm. Inch measurements are mine and rough; the metric one is from the handbook.
The bath is immediately above the kitchen where the boiler is situated, so I do not think there is a long run to contend with, if that is relevant.
In your opinions are his suggestions valid ones?. The power flush is expensive for us, and even more expensive is a new boiler at around £2200. That is if a new boiler would even be practical, seeing the current one is built in to a cupboard type casing, and from my research quite slim line.
Protherm 80e
Flow rate @ 30 deg C temperature rise ….11.2 l/min
@35…………………………… 9.6 l/min
Minimum water flow……………………….2 l/min
Max/min supply pressure……………………6/1 bar
Full technical details are at
http://www.postimage.org/image.php?v=gx1mujcr
The boiler has never seemed particularly good on the DHW side, and that applies especially to running a hot bath and various things have neen done to make matters more satisfactory
10/11/05 replaced air in expansion vessel
28/11/05 replaced faulty plated
15/12/06 service note “pressure vessel may require recharging, not very good”.
12/02/07 re-pressurised expansion vessel, cleaned prv
18/02/08 replaced DHW diaphragm.
None has been particularly effective. We can only run a bath at a very slow rate, no more than a 10 deg twist f the taps beyond which water runs hot and cold.
We recently consulted a local engineer, who suggested that a power flush (£450) might be the solution, but also that the boiler was likely inadequate for us.
We are the two occupants and as well as DHW the boiler serves
2x26" double radiators; 2x33" doubles; 1x63" single; 1x44" single;
1x26" low level that goes under kitchen breakfast corner. double will grille on top; hated towel airer 600x1150 mm. Inch measurements are mine and rough; the metric one is from the handbook.
The bath is immediately above the kitchen where the boiler is situated, so I do not think there is a long run to contend with, if that is relevant.
In your opinions are his suggestions valid ones?. The power flush is expensive for us, and even more expensive is a new boiler at around £2200. That is if a new boiler would even be practical, seeing the current one is built in to a cupboard type casing, and from my research quite slim line.