Combi hot water problem

Joined
5 Mar 2007
Messages
4
Reaction score
0
Location
Angus
Country
United Kingdom
I have a Potterton 24 combi which is 3 years old. It has no problem providing heating but has an intermitent problem where it doesn't provide water of a high enough temperature at the bath. The boiler comes on okay when the tap is turned on but you can't always have a bath due to the low temerature. I would be grateful for any suggestions.
 
What is the hot water like at the other taps?

If boiler is a few years old and it has been fine up until recently then it could be a scaled heat exchanger
 
My conclusion is the flow rate is sometimes too high at the bath to heat the water enough. Turn down the flow rate!

I am speculating that variations in supply pressure due to area or neighbour demand is causing different flow rates at different times.

Your boiler will only heat 8 litres per minute!

Can you measure the flow rate to this bath tap?

Tony
 
The boiler is a Potterton Performa 24 to be precise. I will try reducing the flow rate at the bath.
 
If for the past 3 years your hot water has been fine at the bath hot tap and recently the temperature has got worse then this is due to a lightly scaled heat exchanger regardless of the basin and kitchen tap. Cranking the flow rate down will work but it will shorely get worse over time. If the bath tap has always been poor since day 1 then the flow rate is highly likely to be the probelm at the bath tap.
I doubt you have a scale inhibitor on the cold mains supply to the boiler.

:wink:
 
kevplumb said:
balls try 9

The boiler can only manage about 8 litres per minute in this context. Of course at 35°C rise it will give 9.3 li/min

People expect to fill a bath with water at about 45°C to take account of loss of heat in heating the bath itself and cooling during the 10-15 min waiting until its full.

With water coming in at about 5°C that requires a temperature rise of 40°C and so the boiler will only give about 8 li/min.

Tony
 
How terribly inaccurate you all are.
Potterton claim 9.8 litres/min with 35° rise
The flow restrictor is 10 l/min.

Any more than 7 for a bath and you're doing OK!
 
I have reduced the flow rate and the temperature increases. I think this may be the problem, however I have to reduce the flow substantially for the temperature to rise significantly. This is not a problem I have had in the past.

Thanks for the responses
 
Perhaps the incoming water temperature has not been so cold before?

Why not measure the flow rate in litres per minute so we can confirm that we are correct.

Re Chris's posting that Potterton "claim" 9.8 li/min at 35°C we all suspected that potty didn't understand physics. Odd that they got it right before on the Lynx and Puma though! Perhaps they got a new writer?

Tony
 