condensate pipe/prv

Joined
10 Oct 2006
Messages
24
Reaction score
0
Location
Cumbria
Country
United Kingdom
Hi guys just had a boiler installed by a corgi plumber but im not so sure he has fitted the Pressure relief pipe and the condensate pipe properly, they are both fitted to the waste under the sink before the waste trap, I was under the impression that the pressure relief pipe should vent to the outside and that the condensate pipe can go to the waste pipe under the sink but join after the trap. am i right ? cheers guys and have a good new year Regards Cris
 
Sponsored Links
Yep, sounds like you're right to me.
Check the mfrs instrs on the condensate - sometimes they vary.
 
In theory blow of pipe should be visible but that depemds if you have eagle eyes.
Condensate is down to mfi and seldom needs a trap between boiler and where you tee... AS it is built into boiler
 