Dear @SirLancelot when the electrician did the work, he should have provided an installation certificate. This will have a schedule of test results. This schedule will state the size of cable installed.
If it was 4mm² then a 30A MCB is fine. If it is 2.5mm² then 20A MCB is needed.
As above. The circuit should be RCD protected, it isn’t.
If you have an installation certificate that says the installation complies with BS 7671 then it doesn’t.
If it was 4mm² then a 30A MCB is fine. If it is 2.5mm² then 20A MCB is needed.
As above. The circuit should be RCD protected, it isn’t.
If you have an installation certificate that says the installation complies with BS 7671 then it doesn’t.