A few reasons that immediately spring to mind:
small switch circuit for example a photocell controlling a large lighting circuit,
volt drop,
switches not designed to switch highly inductive loads.
convenience - for example in a shop, you can have a "last man out" key switch by the front door which operates every light in the store, and with a few more contactors, all the non-essential circuits too. Instead of a switch, you could use a timer.
In a house, you could use a contactor to apply power to a fan on the lighting circuit, when the shower switch is pulled.
Contactors are sometimes used on large fridge projects, where a small LCD temperature controller is required to bring online several 3 phase compressors and the like.
If the lights were spread over 3 phases then the feed from the protective device(s) would come straight into the top of the contactor.From the bottom of the contactor the phases would go out to the lights (neutral(s) straight out from the DB)
From one of the phases a control phase is taken to a switch.This switch then switches on the small load of the contactor coil rather than the lights.The contactor will require a direct different phase to the other side of the coil if 400V or a neutral.
The disadvantage of this system is that if you lose the control phase you lose the lot.If any emergency lighting is required then it should be off the control phase.
If the lights were spread over 3 phases then the feed from the protective device(s) would come straight into the top of the contactor.From the bottom of the contactor the phases would go out to the lights (neutral(s) straight out from the DB)
From one of the phases a control phase is taken to a switch.This switch then switches on the small load of the contactor coil rather than the lights.The contactor will require a direct different phase to the other side of the coil if 400V or a neutral.
The disadvantage of this system is that if you lose the control phase you lose the lot.If any emergency lighting is required then it should be off the control phase.
Good point that. Our shop lost a phase all night a week or so ago. a few rows of lights went out, control phase for the contactors was still online. However, the emergency lights discharged themselves within 3 hours, and when all the power was cut the next day, no EM lights
Is this a reg or just a suggestion then, re. the EM lights?
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local