Leaving aside the question of CPCs in another thread.
As far as bonding is concerned it is generally stated/accepted that the swa has to be approximately 8.5 times greater as it must have the equivalence of copper.
This is, though, based solely on the resistivity comparison of copper and the armour. Steel has varying values for resistivity so I assume someone has determined this value to be correct for the armour type.
However, as pointed out in the other thread, the 'k' values of copper and steel are 115 and 51 respectively.
These values have a ratio of 2.255:1
This value corresponds to the charts published for csa comparison (K2/K1 x swa csa) which are discounted as not adequate for the bonding requirement.
Would it therefore not be correct to use this figure, 2.255, when determining the required csa of the armour when used as bonding as the actual resistance is not a consideration?
Or, on the other hand:
As the bonding conductor size is to allow for the heating of the conductor that may be encountered and this is dependent on the resistance, should the steel not be required to be 8.5 x 2.255 = 19.17 times that of copper?
As far as bonding is concerned it is generally stated/accepted that the swa has to be approximately 8.5 times greater as it must have the equivalence of copper.
This is, though, based solely on the resistivity comparison of copper and the armour. Steel has varying values for resistivity so I assume someone has determined this value to be correct for the armour type.
However, as pointed out in the other thread, the 'k' values of copper and steel are 115 and 51 respectively.
These values have a ratio of 2.255:1
This value corresponds to the charts published for csa comparison (K2/K1 x swa csa) which are discounted as not adequate for the bonding requirement.
Would it therefore not be correct to use this figure, 2.255, when determining the required csa of the armour when used as bonding as the actual resistance is not a consideration?
Or, on the other hand:
As the bonding conductor size is to allow for the heating of the conductor that may be encountered and this is dependent on the resistance, should the steel not be required to be 8.5 x 2.255 = 19.17 times that of copper?