Hi folks,

I have a Worcester Danesmoor 20/25 boiler. Yesterday it started locking out when I put the heating on. The amount of time between boiler firing and locking out varies but can be as short as five minutes.

Putting the water heating on does NOT cause the boiler to lock out.

Pipework is S-Plan, water pump is working ok and valve actuators replaced a few months ago.

Can anybody advise?
 
Joined
19 Jul 2007
Messages
5,851
Reaction score
1,119
Country
United Kingdom
Solenoid coil 99% of time.
The boiler does not differentiate between water and heating. It fires when energised.
 
Sponsored Links
Joined
29 Nov 2009
Messages
2,239
Reaction score
548
Location
Shropshire
Country
United Kingdom
As above. Maybe it runs on H/W if you switch it on first, or it cycles, whereas on Heating you look for continuous running.
 
Joined
23 Sep 2002
Messages
247
Reaction score
6
Country
United Kingdom
Thanks both, that's helpful. To your point, Terry, that's what confused me. I would expect it to lockout regardless of whether it's HW or CH; but Oilhead's point is well made, that CH and HW have different run profiles.

Thanks for the help!
 