You said:
I understand the rack needs to be properly earth bonded, and that it would need its own separate electrical ring circuit, probably at least around 40Amp 6mm cable, along with a 50amp MCB, and RCD setup
Almost entirely wrong, and you don't know why it's wrong.
It's wrong because the MCB is a higher rating than the cable, so the cable would fail before the MCB trips, thus causing a possible fire hazard. It would not have been something i implemented under any circumstances. And the whole reason for me asking was to find out.
So you'll make design errors, and the design will not be safe and adequate.
I agree, but i thourghly check every aspect of design, and confirm things before implementing it.
So why you have to be so rude, and nasty about it i dont know.
Show me where I've been anything other than honest and correct. Blunt perhaps, but none of it is personal or abusive. I would put it to you that you've been far ruder than I could possibly be in your attempt to mislead people who are giving free advice.
I have had no intention of misleading anybody, and apoligise if i have, I would consider getting somebody to do the job if i feel im not up to it, and dont have sufficient knowledge to do it adequately. But i wouldnt know until i know what kind of setup is required/involved.. if i feel from what ive been told on how to wire it up, i can do it safely then i would go ahead and do it myself.
And although i made an error with that, its not something i would of actioned as i would of noticed it.. as i said previously i always check and check again, to ensure things are done correctly and safely.
Even when the error was pointed out to you, you didn't understand - you
pretended to.
I didnt pretend, i know what the problem was, upon looking at it a 2nd time, as said above the main problem would be, the cable would become overloaded before the MCB trips, so it becomes a possible fire hazard.
You said:
yea i do see the problem lol, because ideally the cable should be the same as the MCB rating
Really? It should be the same? Why don't you tell us
why you think it should be the same?
It should be the same, or the MCB should be rated lower.. so that the MCB trips before the cable reaches its maximum load rating. Making the circuit safer.
FFS. You were all geared up to install a circuit that could supply an electric shower, and just for three computers, albeit large ones.
I wasnt geared up to go ahead and jump in, installing that system, I was just going by the warning sticker on the power supplies, if i knew they was only 4.5amp i would of speced out a lower rated circuit.. admittedly this is incompetant.. but its the reason i came on here to ask.
and if i went ahead and created a circuit which can handle more load than required.. how is that dangerous?.. its excessive yea.. but still safe.
You really don't know? You were going to install a protective device that wouldn't have tripped on overcurrent until at least 40 Amps, supplying some appliances that would normally run at a combined total of about 12 Amps, and you can't see a problem with your approach?