If it's using 4mm² cable, it would seem relatively unlikely that it is a ring, and even less likely that, even if it were a ring, 4mm² would be needed for spurs.I seem to remember MK will take 3 x 4mm² but no where will a socket spec say it will take 4 cables. One of the reasons why it states only one spur from a ring is over three wires one can't be 100% fully clamped.
Yes, I understand that but the question was asked in a DIY forum, hence very probably related to a domestic installation rather than one in a public building, hence my comment that it was "relatively unlikely" that it was a 4mm² ring, even though it's obviously not impossible.I have a building where all the RFC's are wired in 4mm, this is common practice in public buildings.
You mean you have managed to get four 4mm² conductors into the terminals? Would you be prepared to share with us the reason that this need arose - since, as has been implied, it would be a pretty unusual situation in a domestic installation?Sorted it..Thanks
As has been said it's possible with at least some sockets, probablly most but as the number of wires in a terminal increases so does the risk of uneven clamping forces. This is especailly true with mains wires which have thick insulation.Is it possible to get 4 x 2.5 twin & earth into a 13 amp dbl socket (ie are the terminal holes not big enough)?
IIRC last time this was discussed it turned out that the "rules" on spurs were actuallly only guidance in an "informative" section of the regs. Furthermore while said guidance didn't show multiple spurs from the same point it didn't forbid them either.It is not impossible, some socket outlets are more accommodating than others, but why do you need to do this?
If you are using as a spur, there are regulations concerning the correct configuration to use and number of unfused spurs from a socket outlet.
Given that diyisfun never mentioned 4mm² and explicitly mentioned 2.5mm (presumablly meaning mm²) that seems like an unlikely interpretation of his post.You mean you have managed to get four 4mm² conductors into the terminals?Sorted it..Thanks
Agreed. Nothing in the regs, even the 'guidance' of Appendix 15, says forbids to spurs having the same point of origin. As you say, it is the absence of such an arrangement in the examples shown in the diagrams in that guidance which seems to lead some people to believe there is such a 'rule'. Some trying arguing on the basis of 'point loading' of a ring - but 2 spurs from one socket is not materially different in that respect from single spurs taken from each of two sockets (or JBs) which are a few inches apart on the ring.IIRC last time this was discussed it turned out that the "rules" on spurs were actuallly only guidance in an "informative" section of the regs. Furthermore while said guidance didn't show multiple spurs from the same point it didn't forbid them either.If you are using as a spur, there are regulations concerning the correct configuration to use and number of unfused spurs from a socket outlet.
Oh Dear Most of what I've been writing was irrelevant - I was 'thrown' by eric's talk about 4mm ² and hence didn't notice that the OP had refered to "2.5mm". My apologies to everyone. Even though it's not ideal, 4 x 2.5mm ² conductors is a doddle in many/most sockets, even if they are not 'rated' for that.Given that diyisfun never mentioned 4mm² and explicitly mentioned 2.5mm (presumablly meaning mm²) that seems like an unlikely interpretation of his post.You mean you have managed to get four 4mm² conductors into the terminals?Sorted it..Thanks
Fair enough! However, as I've just admitted, I've been talking relative nonsense because I didn't read your initial message properly. I thought you were taking about 4 x 4mm² cables - which would be very unusual in a domestic situation. Whatever you have done with 4 x 2.5mm² ones quite probably is no different/'worse' than what many (most?) of us have done at times.If I said what I done you would all be B$%$£$%ing me. So lets say its done working & safe.
If I said what I done you would all be B$%$£$%ing me. So lets say its done working & safe.
Glad you believe that it is 'working and safe'. Someone may well ask what tests you have undertaken in order to confirm that it is 'safe'
There's no harm in asking what is a perfectly valid question. The problem is, of course, that we know what would be the truthful answer in the case of the vast majority of DIY electrical work - so I'm not convinced that much is often achieved by asking the question.Just out of real concern for yourself, your family, your pets, your property, your guests, your neighbours, your neighbours family, pets, guests, property etc.. How did you prove the work is safe There you go John, I will ask, just hope some poor b*****r don't get hurt!Glad you believe that it is 'working and safe'. Someone may well ask what tests you have undertaken in order to confirm that it is 'safe'