That particular link to Schedule 2B, is incomplete and therefore misleading without the additional footnotes for each item.
"Replacing the cable for a single circuit only, where damaged, for example, by fire, rodent or inpact"*
* "Providing that the replacement cable has the same current-carrying capacity and follows the same route".
Presumably the ratings at 230V and 240V, so 42-44A.The saga continues. After having bought some 6mm2 and removing the shower, I can now see the shower is labelled 9.6 - 10.5 Kw.
It's borderline, but given the route you describeI'm guessing a 16m run of 6mm2 with this shower is a no no?
6mm² would be just about OK, subject to it not getting much above 35°C in the loft, the airing cupboard or next to the hot pipes.- 5 meters in loft, lying over (but in contact with) insulation. If I replace the cable I could probably make it so it doesn't touch it.
- 2 meters in airing cupboard
- 2 meters under floorboard, some of which about 30cm from hot water pipe
- 7 meters clipped to garage wall
Yup.If so, pretty sh** that the electrician hired to do the job 5 years ago wired it in like that.